Check out this one, picture taken while standing in the walkway between the kitchen and breakfast nook. Sink faucet is visible at other side of the bar.
Outlet is about 12 inches below the underside of the bar and about 27 inches above the floor.
Does this outlet serve the kitchen countertop?
Or does it only serve the bar top?
Or does it serve neither?
Yeah, if it’s within the dimensional limits that it would be considered as a receptacle serving the countertop (no greater than 6" overhang, no lower than 12"), it does require GFCI protection.
When I see colors mis-matched like that cable jack is (ivory or light almond device with a white cover), it makes me look at stuff extra hard. That’s the sign of a handy man.
They look to be 12 inch tiles on the passover portion so if the wall is framed with 2X4’s and then sheetrocked that outta leave about 6 inches (or less) on the receptacle side (the measurable ‘overhang’ area).
I’d go with a GFCI recommended upgrade if it isn’t as it (from the pics) certainly could ‘serve the counter top area’…:mrgreen: