mkoester
(Michael Koester, CMI FL HI-8530)
March 19, 2015, 8:24pm
Installed in 2007 - thank you
mkoester
March 19, 2015, 9:36pm
3
Thanks Mike
From what I can tell, that explains the glazing. But are these Wind Mitigation Form compliant for large missile impact?
It does state "Glazing material successfully passing the impact test of a 48 inch drop height, a 400 pound impact, is classified as “Category 11” - which these doors are.
mlarson
(Michael Larson, WI Lic. # 1672-106)
March 19, 2015, 9:46pm
4
I live in WI. I Don’t know much about wind mits… sorry
A. Exterior Openings Cyclic Pressure and 9-lb Large Missile (4.5 lb for skylights only) All Glazed openings are protected at
a minimum, with impact resistant coverings or products listed as wind borne debris protection devices in the product approval
system of the State of Florida or Miami-Dade County and meet the requirements of one of the following for “Cyclic Pressure
and Large Missile Impact” (Level A in the table above).
Miami-Dade County PA 201, 202, and 203
Florida Building Code Testing Application Standard (TAS) 201, 202, and 203
American Society for Testing and Materials (ASTM) E 1886 and ASTM E 1996
Southern Standards Technical Document (SSTD) 12
For Skylights Only: ASTM E 1886 and ASTM E 1996
For Garage Doors Only: ANSI/DASMA 115
A.1 All Non-Glazed openings classified as A in the table above, or no Non-Glazed openings exist
A.2 One or More Non-Glazed openings classified as Level D in the table above, and no Non-Glazed openings classified as Level B, C, N, or
X in the table above
A.3 One or More Non-Glazed Openings is classified as Level B, C, N, or X in the table above
B. Exterior Opening Protection- Cyclic Pressure and 4 to 8-lb Large Missile (2-4.5 lb for skylights only) All Glazed
openings are protected, at a minimum, with impact resistant coverings or products listed as windborne debris protection devices
in the product approval system of the State of Florida or Miami-Dade County and meet the requirements of one of the following
for “Cyclic Pressure and Large Missile Impact” (Level B in the table above):
ASTM E 1886 and ASTM E 1996 (Large Missile – 4.5 lb.)
SSTD 12 (Large Missile – 4 lb. to 8 lb.)
For Skylights Only: ASTM E 1886 and ASTM E 1996 (Large Missile - 2 to 4.5 lb.)
B.1 All Non-Glazed openings classified as A or B in the table above, or no Non-Glazed openings exist
B.2 One or More Non-Glazed openings classified as Level D in the table above, and no Non-Glazed openings classified as Level C, N, or X
in the table above
B.3 One or More Non-Glazed openings is classified as Level C, N, or X in the table above
btoye
(Bradley Toye, CMI)
March 19, 2015, 9:47pm
5
What Mike posted (first) has little to do with large missile impact testing and compliance with the 1802. On your glazing etching, the DCA (Dade County Approved) and LSG (laminated safety glass) indicates that the glazing is rated. But, to be fully compliant, you should be looking for a rating sticker on the unit frame.
Then you are both wrong. The interlayer used by PGT has 3 different thicknesses that are all MDCA approved…but only 1 of which is impact rated.
MDCA could mean one of three different approvals have been meet…or all three, which would classify it as impact rated.
Pull the NOA for the window and research the type of laminate used. Or, just learn how to read the label, it’s written right on it 4th line down.