Fact:
Hood fans in dwelling unit kitchens are permitted to be cord and plug connected, but must be supplied by an individual branch circuit.
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
Originally Posted By: lkage
This post was automatically imported from our archived forum.
--
"I have never met a man so ignorant that I couldn't learn something from him."
Galileo Galilei
Originally Posted By: whandley
This post was automatically imported from our archived forum.
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
Originally Posted By: whandley
This post was automatically imported from our archived forum.
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
Quote: |
422.16(B)(4) Range Hoods. Range hoods shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for use on range hoods in the installation instructions of the appliance manufacturer, where all of the following conditions are met:
(1) The flexible cord is terminated with a grounding-type attachment plug. Exception: A listed range hood distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug. (2) The length of the cord is not less than 450 mm (18 in.) and not over 900 mm (36 in.). (3) Receptacles are located to avoid physical damage to the flexible cord. (4) The receptacle is accessible. (5) The receptacle is supplied by an individual branch circuit. |
Quote: |
2005 NECH Commentary:
Section 422.16(B)(4) was added to the 2005 Code to allow range hoods to be cord-and-plug-connected under five specific prerequisite conditions. A grounding-type attachment plug is not required where the range hood is identified as protected by a system of double insulation. One method of verifying such protection is to look for the mark of a testing laboratory. |
Quote: |
210.11(C)(3) Bathroom Branch Circuits In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2). FPN: See Examples D1(A), D1(B), D2(B), and D4(A) in Annex D. |
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: cbuell
This post was automatically imported from our archived forum.
Originally Posted By: whandley
This post was automatically imported from our archived forum.
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
whandley wrote: |
OK Joe, I get it now. This was a test! I'm thinking dedicated circuit, but your original post states branch circuit. Branch circuits can have multiple outlets and or small appliances on a common branch circuit. So the range hood can have a cord and plug system, but must NOT have anything else plugged into that individual outlet. That would also allow us to have multiple bathroom outlets on a common GFCI protected branch circuit. Is this correct?
http://www.statefarm.com/consumer/vhouse/articles/overload.htm Thank you again. I believe the state of california may now be code compliant  |
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: whandley
This post was automatically imported from our archived forum.
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
–
Joe Tedesco, NEC Consultant