Anything particularly dangerous with these vs the distribution panels?
That GEC shouldn’t be split for the heatpump & enclosure, correct?
Is this missing a dead front? The other disconnect box also looks like this and I called it out, but now I’m noticing there isn’t anywhere to attach a dead front.
I am curious what this transformer is all about. They just hot wired it off this switch gear and threw on a 15 amp fuse protection and called it good. I do not think this is up to industry standard, eh? Thoughts?
This is 3Ø, 3 pole, 60 amp, non-fused, disconnect switch. They’re using the stripped white conductor as an EGC and have tapped off of one leg to fed a transformer via a 15 amp fuse. That transformer requires a neutral not a tap to the EGC. The connection to the enclosure is also incorrect.
Is this a joke? A blind man can see the deadfront cover. Do you even know what “Deadfront” means? Close the cover and try to stick your fingers where there are energized conductors or components.
True or false: the majority of electrical panels that you inspect have both a front door and a dead front cover, regardless of the fact that shutting the front door conceals wiring connections?
If you don’t deal with a lot of knife switch external handle disconnects, you can excuse him for thinking a cover might be missing. Most homes don’t have that type of disconnect. Every factory I’ve been has those types so I had to think about it for a second to realize what he was suggesting.
The disconnect handle is on the outside, you can see the switching mechanism on the inside. Don’t expect a dead front here, because the panel door is the dead front.