GEC: Another Free Inspection Related Graphic
ThE clamp needs to be listed for direct burial. It does not need to show under the NEC.
The GEC is shown on the wrong side of the clamp.
And while were on a roll the arrow is pointing to the GEC not the electrode.
Correct. Impalement hazard!
Robert, don’t hesitate to correct any mistakes. Thanks
New attic insulation graphic. The intent of this graphic is to only show the relative difference in some common attic insulation thickness based on R-38.
(I know there are many combinations and ranges for different climate zones.)
Again the conductor is on the wrong side of the clamp and the rod is not flush or below grade.
If you really want to be picky from the NEC busbar is one word.
Concerning spray foam, I would define open cell vs closed cell, the have different R values per inch.
Yes and only one “s”. It appears correct in the original graphic.
I get the feeling Randy is regretting this already, lol.
Back to the panel illustration, it could be improved by showing the grounded conductor attached to the opposite bus bar and show a green bonding screw to indicate bonding with the grounded bus. Just a thought.
And make the neutral white.
Made a couple of modifications. I am going to lets this one cool off a few days.