Originally Posted By: jpeck
This post was automatically imported from our archived forum.
Jeff,
That kinda looks like BX, or maybe 3/8 FMC (flexible metal conduit)
Looking at the photo, either 1) the metal spiral wrap is in the clamp and not the grounding conductor inside it, or 2) the conductor is in the clamp and not the metal spiral wrap.
The problem with 1) is that the metal flexible conduit, which is a spiral wrap, is not rated to be used as a ground path, for basically anything. And that the ground conductor is not connected, which is also bad.
The problem with 2) is that the ground conductor is now covered with a metal shield, which must be bonded to the ground conductor at each end. Also, being as the flexible metal conduit is not rated or approved for use as a ground path, using it clamped to the ground conductor at each end makes it part of the ground path. Part of the ground current will be going through that FMC, like parallel conductors. When you use EMT or rigid conduit for that protection, it is also required to be bonded to the ground conductor at both ends, but they are approved for use as a ground path.
With conduit, you can think of it as one length of metal x feet long. With FMC, you would have to consider it as a spiral wrapped conductor, much longer than what you see, but most importantly, it is spiral wrapped around the ground conductor, making a choke coil.
A choke coil 'chokes' out ac current while allowing dc current to pass. The current which is trying to pass through the choke coil (in the wrap of the conductor itself) is ac, and is ac in the conductor going through the choke coil (the ground conductor). This would try to 'resist' and stop or at least impede the flow you so desperately need at the time you desperately need it. And the more you need it (higher ground current), the more it will impede (choke) itself.
--
Jerry Peck