This hot water heater the TPR attached to a drain system and looks the be connected to the unit above. is my thought process correct.
Electrical wiring connections needs to be inside the top of the hot water tank conduit.
A major defect is a condition of a system or component that renders it non-working, non-performing, non-functioning or unsafe , and requires a professional contractor to further evaluate and repair, correct or replace.
The pipe should not be directly connected to the drainage system;
The pipe should not have valves or tee fittings installed;
The pipe should not terminate more than 6 inches (152 mm) above the floor or waste receptor;
The pipe should discharge to a termination point that is readily observable by the building
occupants; and
Stacey, you can access all the ICC codes (and ADA and OSHA standards) and copy and paste from them for free from a page on my website. That’s where I got the following:
It’s simply a “water heater”, it heats cold water, not hot.
You’re correct, the TPR discharge pipe is improperly executed. What did it connect to at the top?
It needs to discharge through what’s referred to as an air gap, not an air break (what you show in the pic).
Yes, the electrical connection is also sloppy. Ideally an armored cable is used from a junction box, but that’s rarely the case. So at the least it should be covered and held in place by a proper cable connector.
Stacey, there is no reason to define it as major or minor… Just call it a a safety issue/deficiency, explain what TPRV’s function is… and what can happen if those deficiencies are not corrected. This will allow the purchaser to prioritize and have the issues repaired, if at all. Remember, most buyers won’t know what TPRV is.
Like Simon says, I wouldn’t use the term Major, or “Major due to safety” which to me is too vague. I’d say something like:
“The discharge pipe for the water heater temperature/pressure relief (TPR) valve was improperly configured. The TPR valve and discharge pipe form a safety assembly designed to safely discharge hot water in the event that the water heater gas burner fails to shut off in a timely manner. An improperly configured TPR discharge pipe can rupture, causing scalding or burns to anyone nearby. The Inspector recommends correction by a qualified plumbing contractor.”
or simply:
“The discharge pipe for the water heater temperature/pressure relief (TPR) valve was improperly configured. This condition is a safety issue and should be corrected by a qualified plumbing contractor.”
The first one conveys more of a sense of urgency, but some inspectors like to keep things as short as possible. Either one should go into the summary.