Originally Posted By: jpeck This post was automatically imported from our archived forum.
Russell,
I think Ryan was thinking of metal duct, not flex duct.
You are correct. Flex duct is not allowed to be run through a ceiling, floor or a wall. It needs to be transitioned to rigid (like duct board) then back to flex duct.
When you get the book, go to page 20, Section 6, 6.2
d. When installed in a fire-rated floor / roof ceiling assembly, ducts shall conform with the design of the tested fire-resistive assembly.
g. Should not penetrate walls where fire dampers are required
And everyone knows that all concealed spaces are to be closed off for draft stopping and fire blocking purposes, such as at floors, ceilings, walls, top plates, bottom plates, etc.
So I guess a flexible duct going through a wall would be debatable as someone could argue that IF you could seal around the flexible duct (and not have the flexible fall away from the sealant), you could penetrate through the wall. However, the other side would argue that flexible duct, being flexible, will eventually fall away from the cut opening, leaving a non-sealed opening between the duct and the cut opening's edge.
From the Florida Building Code.
M603.5.5 Penetrations prohibited. Flexible air ducts and flexible air connectors shall not pass through any fire-resistance-rated assembly. Flexible air connectors shall not pass through any wall, floor or ceiling.