Is this panel Properly bonded?
Originally Posted By: Kevin Luce
Is the smaller wire with the white tape the “main bonding jumper” for the service panel?
[ Image: http://www.nachi.org/bbsystem/usrimages/w/wel89052.jpg ]
Originally Posted By: jpope
There is no panel bond visible in your picture. Do you have any othe pics?
Jeff Pope
JPI Home Inspection Service
“At JPI, we’ll help you look better”
(661) 212-0738
Originally Posted By: rmoore
Kevin…are you sure this is the service equipment? I don’t see any grounding conductors at the “floating” neutral bar. Can you describe the home and the panel and service disconnect locations?
Richard Moore
Rest Assured Inspection Services
Seattle, WA
www.rainspect.com
Originally Posted By: wdecker
There is a sranded, bare copper wire connected to the frame on the right of the picture.
If I am not sure, I will take a continuity reading between the ground and the neutral and see if they are connected.
Hope that helps.
Will Decker
Decker Home Services
Skokie, IL 60076
wjd@DeckerHomeServices.com
Will, simple continuity may not be enough to prover the service is properly bonded.
You may have an incidental connection that is not sufficient to clear a fault.
You really need to identify the 250-66 sized bonding jumper.
In the case of this panel I don’t see one. I am guessing this is load side equipment (sub panel). The wire going to the enclosure still looks small and it does not terminate in a listed lug.
110.14(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Agree, Greg;
Just trying to be a smart butt. Guess I should have used an icon.
Will Decker
Skokie, IL 60076
No problem Will.
I may beat the grounding horse too hard but it is the basis for virtually every other safety device in the system.