I inspected a main panel today where the terminal bar was bonded to the cabinet. The neutrals are isolated, however, there is no green bonding screw visible to bond them to the cabinet. It appears to me as though the cabinet is wired as a remote when it’s actually the main. Is this ok? In my mind it’s not correct due to an unidentified bonding/grounding issue, I just can’t identify the issue as I’m not a qualified electrician. I’m hoping someone has seen this before.
The wire you mentioned crosses the bottom of the cabinet and connects to the other terminal bar. So, going forward, if the copper wiring coming out of the neutral terminal is connected to a terminal bar, then that’s ok?
The neutral, EGCs’, and panel enclosure should all be bonded at the first point of disconnect after the service. There are many ways to accomplish that. I can’t say I know exactly every method that is or is not allowed though.
Looks possible. If you are in a pinch, I would write it as “could not verify bonding of EGCs’ and panel enclosure to service neutral at the first point of disconnect due to items in panel blocking full observation.” Or something like that.
No, if this is indeed the first disconnect, it must be bonded.
As mentioned, it is possible that the bonding is done with the copper conductor, but square D panels all have a bonding screw on the neutral bar. It’s missing, upper left.
You also have that double tap at the neutral lug, and I always call out the lack of sleeve/protection on the overhead service lines as a safety hazard.