Those are very kind words and I thank you. Robert…it would not matter as that enclosure and probably the panelboard is only listed for 150A and while it may be just the service disconnect possibly I am sure it also serves to meet 230.90 as well. Home Inspectors should note anything that appears out of place…never assume…and defer to electrical contractors when needed.
I love this old label…even directs the installer to not increase the main circuit breaker rating beyond what is installed…excellent label and in great condition.
You’re correct. I was only asking since if there were a 150 amp OCPD upstream this would still be a violation but not as big of a hazard. Although the 200 amp CB in the panel rated for 150 amps would be non-compliant, the buss and condcutors would not be subject to overload if there were a 150 amp upstream OCPD.