Multistrand Aluminum main feed vs. branch and insurance

Has anyone had an issue recently with the Citizens form multistrand box? It is always marked yes 98% of the time due to the main service feed…

We are getting calls now re. the range, furnace, dryer high amp usage appliances that have multistrand aluminum and insurance won’t cover those.

Anyone have an idea on how to talk to Citizens and get them to change the form to allow main feed only?

I have tried callind the FL Office of Insurance Regulations in the past and never get anywhere.

Is it Citizens that won’t insure properties if the multi-strand aluminum box is check or is it some other insurance company? A problem with the 2018 4-Point was that inspectors were checking the aluminum checkbox if there was any aluminum wiring, whether single-strand or multi-strand aluminum. The multi-strand box was needed but it took them seven years to do the update.

Citizens isn’t likely to change the form any time soon. The form doesn’t need to be changed. The people who are reviewing the forms need to be better educated. Aluminum multi-strand is safe and has been the most common large conductor material for more than half a century.

The new 1802 form was supposed to go into effect at the beginning of this year. Now it’s been pushed back to April 26 of 2026. The wheels turn very slowly at Citizens. There was a seven year interval between 4-Point updates and 14 years between 1802 updates (assuming the new 1802 goes into effect in April).

2 Likes

Morning, Mike. Hope to find you well.

Although I am not situated in FLA, and did not use Citizens insurance, I can’t count the amount of stand al cables I inspect in homes.

Are clients calling you back about this?
You see this being a point of liability contention for inspectors in Fla?

2 Likes

Same here in Oregon…. I can’t remember the last time I saw anything but stranded al for range, dryer, etc. on a house build in the last 40 years.

2 Likes

We are not sure… they did not say…most likely it is other carriers but could be Citizens as well. This seems to be something that is now developing that was never a problem in the past.

Educating the personnel who review these reports is definitely needed, however there are numerous other issues besides this one that they need to learn about and understand (as well as on the wind mit. form). Too much to discuss in this thread.

I guess for now we will have to identify/explain which exact circuits are multi-strand and let each carrier decide from there.

If they won’t accept any multi-strand aluminum then they aren’t going to have many customers.

2 Likes

Hi Robert,

We had two calls about this issue just yesterday out of the blue. Never was an issue before…
Now we have had a couple of instances where the insurance customer service rep. in the local agency called us with confusion thinking we were talking about the single strand aluminum which is a known hazard.
We had to explain the difference, etc.

This issue is raising concern for us because we have hundreds of reports on the new March 2025 form where that box is checked.

1 Like

It is very common in homes and has never come up before until the Citizens 4-Point report form changed March of this year.

1 Like

Multi strand AL has never been a problem. In fact multi strand AL is almost 100 % used in hydro installations. Why mention/consider it at all? Cheers

3 Likes

image.pngThe form requires we mark all wiring types that are present

1 Like

Multi-strand aluminum will not prevent anyone from obtaining insurance. There are two things that could potentially be happening here. The most common thing I see are agents that are saying that this will be an issue with insurance and refusing to send in the report. They often will say that underwriting pushed it back even though they didn’t send it in the first place. Agents will get dinged for sending in reports with issues on the report and if this happens enough they will not be allowed to write for citizens for a period of time. The only other option is that the report was reviewed by a new underwriter that is not competent enough to know the difference, in which case the agent should be able to push back. I have copies of the most up to date underwriting guidelines for citizens and it specifically excludes Multi-strand aluminum wiring from preventing one from being able to obtain insurance. Hope this helps.

1 Like

As far as the main feed wires are concerned. My 4-point report is set up to distinguish between SEC and branch wiring. Then there is a section in it that states what the branch wiring is used for if Multi-strand is present. I do not use the citizens form though, oddly enough my form has had the section in it for the past 7 years that says “ If Multi-strand is present indicate it’s use..”. Everyone was talking about the new form and I was so confused because I didn’t see the difference.

1 Like

We agree 100%
Can you send us a copy of those guidelines please?

Thanks,
Mike

1 Like

2 Likes

Hope this helps

1 Like

It’s a 4-Point requirement. The previous 4-point only had one checkbox for aluminum. It now has two to differentiate between single and multi-strand. The update was needed because the single checkbox created confusion. The cloth wiring change has also cleared up a lot of confusion.

1 Like

Thank you very much!

The wheels turn slowly for most all insurance companies, unless it involves their premiums & bills going up, SIGNIFICANTLY, it seems…

1 Like

Maybe that’s their goal. A few years ago, our mortgage lender failed to pay a very small portion of our insurance from escrow. It was something like $8. They canceled our insurance instead of giving us an opportunity to pay the $8. My insurance agent said that they were looking for any excuse to cancel policies because they didn’t want to sell homeowners’ insurance any more but they couldn’t cancel without a reason because of insurance laws.