Originally Posted By: jpope This post was automatically imported from our archived forum.
Tim,
Did you catch the fact that this is a Zinsco panel board? The AL/CU splice may be much less critical than the potential defects/deficiencies that are common in Zinsco panels.
Any time you see this type of splice (IMHO), it should be verified by an electrician. Anti-oxidant is required at the splice and the wire nut should be listed for CU/AL.
Strange that they would do this as Zinsco breakers are listed for AL as well as CU.
-- Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738
Originally Posted By: thejnicki This post was automatically imported from our archived forum.
Thanks Jeffrey,
Yes i did notice the Zinsco panel, I also let them know that they installed the wrong type dead front cover which would not seat properly (Sylvania cover). Thanks for the reminder Jeffrey.
Whats your opinion about the 2 differnet wire sizes?
Originally Posted By: jpope This post was automatically imported from our archived forum.
thejnicki wrote:
Whats your opinion about the 2 differnet wire sizes?
The wire size is appropriate for the ampacity. If the connection is made properly, the difference in conductors should not be an issue.
The Sylvania cover was probably correct, just didn't fit properly. Late 70's through early 80's was when Sylvania bought out Zinsco and adopted their garbage. All they did was change the sticker.
The next cross-over was the Sylvania/GTE.
All Zinsco's - just different names.
-- Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738
Originally Posted By: mcyr This post was automatically imported from our archived forum.
I do not want to sound stupid or something, but if my understanding is correct, aluminum wiring is always one size up from copper for the same amperage.
So, if a 14 gauge copper conductor is fused at 15 amps, the same conductor in aluminum should be 12 gauge and still fused at 15 amps.