Need Input

Originally Posted By: hgordon
This post was automatically imported from our archived forum.



When can these be used…or cant they?


![](upload://jlZGfbARB3TYOv3HxLKQlvo8Shl.jpeg)


Now what about these TAP-INS?

The main feed is Aluminum 2/0...


look at the pic below, they say 1/0 on the tap-in device...anything I should know about this?



Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



The upper picture looks like a foot lug has been jammed into the panel terminal.


That is definitely a violation.

The other two pictures of insulation piercing connectors may be fine.

The use of these inside the enclosure is fine, what I do not know is what they are feeding and the where the overcurrent protection is for the tapped conductors.

You say the main feed is 2/0 AL and it looks like the connector says 1/0 to 8.

A couple of questions

1) Did you see that the wire leaving the breaker is 2/0?

2) These connectors should have two ratings one for the tap and another for the run.

example

Run 4/0 to 1

Tap 1/0 to 8


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



I went to the Ilsco web site and if these connectors are made by Ilsco it is not looking good.


http://ebusiness.ilsco.com/webapp/wcs/stores/servlet/CategoryDisplay?storeId=10001&langId=-1&catalogId=1&categoryId=151

The only one with a 1/0 to 8 rating is the for the Run

An Ilsco IPC-1/0-2 is rated 1/0 to 8 run and 2 to 8 tap.

It is possible these in the picture are another brand.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: hgordon
This post was automatically imported from our archived forum.



As far as who the manufacturer is…or any additional info…does this foto help?





They are feeding a subpanel which powers the pool pump, sprinkler pump, and pump fopr the jaccuzzi in the pool.



heres a view of the inside


I could not identify where the double tap went...


note the "crimp" marks on the feeder to the sub-panel...


Look at this neutral...



Originally Posted By: Brian A. Goodman
This post was automatically imported from our archived forum.



I see “ITT” on that piercing device, who used to own “Blackburn”. By now who knows.


I've never seen anyone stick a mechanical lug in a terminal lug like that before. Gives the term "double-lugging" new depth. Bob's right of course, not acceptable.


Originally Posted By: hgordon
This post was automatically imported from our archived forum.



So…can some of you more electrical type folks give me the call out verbage on this?


I dont want to tell them how to fix it...just want to report the facts here.


Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Hopefully JP will step in, I am sure he would know the right way to put it.


A little more here, am I correct that the 8 AWG tap of the 200 amp feeders go to feed the small panel on the left. Then they are tapped again with 10 or 12 AWG to feed something out of sight?

You have some major defects here that need to be addressed.

Jerry where are you? ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Just start listing what you saw:



  • improper multiple taps - check all neutral, ground and hot terminals for proper terminations and connection
  • improper bolt on taps
  • charring / melting insulation on neutral conductor with overheating evidence on conductor
  • etc.
  • correct any other improper wiring conditions found or created while making the above corrections.



--
Jerry Peck
South Florida

Originally Posted By: hgordon
This post was automatically imported from our archived forum.



Hey Jerry…after Frances blows by…wanna get together for coffee?


I dont have my nextel any longer...want my cell number?


Originally Posted By: jpeck
This post was automatically imported from our archived forum.



hgordon wrote:
Hey Jerry...after Frances blows by...wanna get together for coffee?

I dont have my nextel any longer...want my cell number?


Sure, e-mail me.

I don't know what my schedule is, other than I have a large house in Jupiter to do (was scheduled to do it Wed. but the builder and I figured we might as well wait until after the hurricane to check it out). Then I may have some re-inspections starting to come up in an area where I did 1 year warranty inspections and they had major problems, Frances may have exposed some of those problems I brought up and the builder pooh-pahed.

I've got to check with Lois when she gets back on Tuesday (she live in Palm Beach Gardens and left town Friday to avoid the hurricane) to see what my schedule is.

The rest of this weekend I've gotta bust my butt on these reports for over at Port Charlotte and Punta Gorda.


--
Jerry Peck
South Florida

Originally Posted By: hgordon
This post was automatically imported from our archived forum.



OK…same here.


By the way..set aside Thursday the 16th...that wil be our next Chapter Meeting.


Originally Posted By: jpeck
This post was automatically imported from our archived forum.



hgordon wrote:
OK...same here.

By the way..set aside Thursday the 16th...that wil be our next Chapter Meeting.


How about we make it Tuesday the 7th? So we can join the meetings together? If not, I will check on Thursday the 16th, but will keep trying to combine them.

That is my ultimate goal, making a local meeting FOR ALL local inspectors and why I am 'separating' the ASHI part out of it.


--
Jerry Peck