On one of my inspections today; there was an updated service panel. The 60 amp two pole GE breaker was 178 f. I didn’t think to check the amps at the time (brain fart). It controlled the electric furnace that was running at the time. Oh, and the rest of the panel was between 80-85 f.
Any thoughts. Any comments would be very helpful.
A 90 degree Delta T is way too much, in my opinion I would even consider that high if the breaker was GFCI or AFCI, call it out for further evaluation.
I did call it out, however for educational purposes,does anyone have thoughts on possible causes? Do you think it could just be a defective breaker? I have never had this problem with GE breakers. Square D occasionally, FPE all the time; never GE. My second guess was a problem with the furnace (wish I checked the amps).
JP,
Thanks, but the conductors were #6
The panel had been recently updated (maybe 1 year old). I have sometimes seen discoloration to the contacts one side or both sides of a breaker (from a bad connection). I am thinking that it’s a bad breaker.
Thanks to all.
I regularly used an IR thermometer to check up to 1500 amp breaker connections and rarely saw them more than 10-15 degrees over ambient.
(Granted, I never saw them at full load!)