Adding a new sunroom off the back of my house, with full windows. I am having a bit of a gentlemens disagreement with the permit inspector about the need for tempered glass in a certain window, and could use help in providing proof that it is not needed.
First off, I am in Ohio, and here is the code I believe we are following:
The pertinent section says:
I believe in my instance, Exception number 3 is in play for the following window:
The bottom line here is… The AHJ has the final say in all code interpretations and allowances for the municipality he/she is employed by. Like it or not, you have no real recourse. A visit with “his boss” may help, but it may also only help in pissing off the people that you need to get your project completed. Choose your battles wisely. IMO, this isn’t the battle to fight. Pay the few extra dollars for the upgraded glass and forget about it.
I believe you are correct. That window would not have to be tempered if the door does not swing into it, and the sill is at least 18" above the floor. If AHJ has a different interpretation, they are required to show you that reference in their local amendments to the building code.
No. There is no reference to door “swing” in the standard and the minimum height at the bottom is 60 inches to qualify for the height exception. It’s to protect against human impact, not impact by the door.
Yes, he has the authority in this situation, but isn’t he wrong?
Exceptions:
" Glazing in walls on the latch side of and perpendicular to the plane of the door in a closed position. "
That window is glazing in a wall that is perpendicular to the door, and that wall is on the latch side. No swinging mentioned in the code, and no swinging door here.
It used to reference door swing. Now it just says latch side…same thing, different side. If any window glazing is less than 18" and more than 36" from the floor, and is >9sf in a walkway, it is a hazardous location. R308.4.2 and R308.4.3
Glazing in Section R308.4, Item 6, in walls perpendicular
to the plane of the door in a closed position, other than the wall toward which the door swings
when opened, or where access through the door is to
a closet or storage area 3 feet (914 mm) or less in
depth. Glazing in these applications shall comply
with Section R308.4, Item 7.
The 2006 commentary expands on the discussion regarding the door swing and includes a diagram - I concede on the swing discussion. Thanks for making the point.
Thought I would close the story on this. Final inspection was this week by a different inspector. I was not here but wrote up my reasoning, and included examples I had found.
No feedback other than it was passed. Works for me!