Service Entrance Meter

I encountered a meter that is so high it cannot be reached without a ladder. Is that acceptable?

Odd, but the homeowner typically has no reason to access the meter, assuming there is not an exterior disconnect at the meter. Do you have a picture or a measurement? If the height is really excessive, it might be worth a mention in the report.

Without a picture I would say yes. The meter is the power companies property/decision. That is unless the main shutoff is at the meter.

Was there by chance a deck or a porch landing previously at that location, below the meter?

1 Like

It was about 9 feet up the wall. The raceway from an underground service conductor runs up to it.

There was not deck or porch at this location. The shut off breaker is inside.

Is it a new build? If so, have they declared grade yet?

Pictures would help…

1 Like

Was this near a flood zone or shoreline? It may have been allowed to keep the meter above flood levels. Up to power company.

2 Likes

No.
——————————

4 Likes

I agree with @gwells.

I say write hard on that one, especially being that the service disconnect was also that high and out of reach.

This is what Google has to say on the subject:

is it acceptable to install an electrical meter with service disconnect 9 feet from the ground? - Google Search

No, it is not acceptable. Installing an electrical meter combo with a service disconnect at 9 feet above the ground violates both national safety codes and standard utility company regulations. [1, 2, 3]

National Electrical Code (NEC) Violations

Per NEC regulations, a service disconnect must be “readily accessible”. This means it can be reached quickly for operation or isolation without requiring a person to climb over obstacles or use a portable ladder. [1, 2]

  • The 6’7" Rule: According to NEC 240.24(A) and 404.8(A), switches and circuit breakers must be installed so that the center of the grip of the operating handle, when in its highest position, is no more than 6 feet 7 inches (2.0 meters) above the floor or finished grade. A 9-foot installation exceeds this safety threshold by over two feet. [1, 2, 3]

Electric Utility Company Violations

While the NEC governs the disconnect switch, the local electrical utility company governs the placement and height of the actual meter socket. [1, 2, 3]

  • The 4-to-6 Foot Standard: For safety, manual reading, and maintenance, most utilities require the center of the meter glass to be mounted between 4 feet (minimum) and 5.5 to 6 feet (maximum) above the finished grade.
  • Denial of Service: If a meter socket is placed at 9 feet, the utility technician cannot safely service or read it from the ground. The utility company will reject the installation and refuse to hook up or energize the power. [1, 2, 3, 4, 5]

Rare Exceptions

The absolute only scenarios where a height exceeding the standard is permitted include: [1]

  1. Flood Zones: If the property is in a designated flood plain, local ordinances or utilities may require the equipment to be raised above the Base Flood Elevation (BFE).
  2. Permanent Platforms: If the meter must be placed high due to structural constraints, a permanent, code-compliant concrete or steel working platform with stairs must be constructed so that the user stands at a level where the handle is still under 6’7" relative to that platform. [1, 2, 3, 4]

If you are dealing with a unique structural constraint or flood hazard, you must contact your local Authority Having Jurisdiction (AHJ) and your electrical utility provider to get a written variance before attempting an elevated install. [1, 2]

1 Like

Around here, the electrician installs the meter box and the raceway to below final grade. The power company pulls their conductors into the meter base and installs the meter.

It seems to me that if the power company installed their equipment, that they were okay with the setup.

An inside and outside photo would add much more context to your inquiry.

I took what Stephanie said to mean “inside” the house.

Maybe she would clarify.

Regardless…it is problematic.

3 Likes

You’re probably right, Larry, I was thinking “inside” the same panel as the meter, since all new construction, if it is, are now required to have an emergency disconnect outside.

1 Like

In flood zones the meter has to be located above the base flood elevation, typically a minimum of 48" above. It may not be unreasonable to see a meter at 10-15’ above the ground. Here in NJ the utility would require a permanent means of access. Typically a set of stairs and a platform in front of the meter will comply with the requirement.

6 Likes

I rarely see them too high but many times have seen them a couple feet above a new deck… The service neutral makes a nice place to hang the metal tongs for your BBQ :slight_smile:

3 Likes