I’m assuming the way they attached the pigtail under the neutral lug is not correct???
There’s a double tap on the breaker to the left, 3rd from bottom.
Neutrals and grounds mixed and/or double tapped with each other.
A neutral and ground double tapped at neutral lug at top right.
Double pole breaker at top right…white wire should be reidentified.
Abandoned wires at bottom of enclosure.
I’ve never seen a panel design this poor…at least not newer ones. ( 1997 )
Neutral and ground bars are nearly right behind the breakers…very hard to see everything.
Anyone care to comment???