1900’s house with fairly recent breaker panel installation. The main breaker is 100 AMP, but the wire from the meter is the old cloth wrapped style and is about 1/2" in width. Does this seem like appropriate size for 100 amp panel?
If it’s cloth wrapped, it’s probably insulated with rubber. I would have no problem recommending replacement of rubber-insulated, tinned-copper if, in fact, that’s what it is. Being a 1900 build, with that old wire, it’s probably set up for 60 amps.
William, there is no such thing (for argument’s sake) as a 125 amp service. Residential services run 100, 150, 200 & 400 (320) amps. Above that is rare.
There are 125 amp rated panels, but this does not equate service to size.
Scott, the meter itself is actually irrelevant. It belongs to the POCO and most all plug in style are 200cl rated. They use the same meter from 100 to 320 amps.
William, there is no such thing (for argument’s sake) as a 125 amp service. Residential services run 100, 150, 200 & 400 (320) amps. Above that is rare.
There are 125 amp panels but this does not equate to service size.
Scott, the meter itself is actually irrelevant. It belongs to the POCO and most all plug in style are 200cl rated. They use the same meter from 100 to 320 amps.
4ga SE might not be much bigger than that. The real answer is to measure the conductor itself. It is very possible that could be 6ga, left over from an old 60a service but you have to measure to know.
Agreed…most of the services I do now are in PVC if possible and we use 2/0CU on all 3 lines ( 200A Service )…due to the increase of harmonics and so on and to be honest because we buy the 2/0 CU in long lengths…but yes the SE usually has the smaller neutral…and Peter is correct they do have SE in equal sizes with all the same size conductors as well.
I looked in the Southwire catalog (the one I have handy) and it looks like all of their SE (3 wire) has a full size neutral. The SER (4 wire) has a downsized grounding conductor (per 250.122)