lfoster
(Linda J. Foster, TREC # 7654)
September 25, 2008, 5:20am
1
Correct me if I am wrong, here. :mrgreen:
-House built mid 60’s, service entrance panel
-Split bus panel
-Another set of conductors are attached on lugs beside the SEC lugs, which are then secured further down the panel. At that second securing, it is a double tapped with a smaller wire connecting to the other opposite side.
This makes all breakers hot (not fed from upper breaker) and exceeds the 6-throw rule.
Right ???
Oh, Stablock panel in hallway. The things we find.!
Thanks for all the input
mroberson
(Michael Roberson)
September 25, 2008, 11:38am
2
Linda, I just recently found a panel similar to this one, maybe this will help .
Check out this panel, No main breaker/shutoff, but 2 60 amp shutoffs that shutoff different sections of the panel. They soldered wire DIRECTLY onto the distribution plates. This house HAD electric baseboard heat, apparently it was removed, that is...
Looks like in that panel you have to throw every breaker?
gbeaumont
(Gerry Beaumont)
September 25, 2008, 12:45pm
3
lfoster:
Correct me if I am wrong, here. :mrgreen:
-House built mid 60’s, service entrance panel
-Split bus panel
-Another set of conductors are attached on lugs beside the SEC lugs, which are then secured further down the panel. At that second securing, it is a double tapped with a smaller wire connecting to the other opposite side.
This makes all breakers hot (not fed from upper breaker) and exceeds the 6-throw rule.
Right ???
Oh, Stablock panel in hallway. The things we find.!
Thanks for all the input
Hi Linda,
Yes that appears to be the case.
Regards
Gerry
lfoster
(Linda J. Foster, TREC # 7654)
September 25, 2008, 1:37pm
4
Michael,
Yes. Would have to throw every breaker.
Thanks,
Linda
Marc_Benz
(Marc Benz)
September 26, 2008, 12:48am
5
Linda .,
You have to defered this to the electrician there is few code volidatons there.
Merci,Marc