This is prep for a stucco patch job… it looks wrong to me. The woven wire is tight to the tar paper leaving no room for stucco to surround it. The staples pull out easily and look like they will rust. And the staples are in the sheathing not the framing. Am I too picky here?
The California Building Code says to use ASTM C1063. ASTM C1053 has notes:
*Table 3 Footnote: B (Woven Wire) Metal plaster bases shall be furred away from vertical supports or solid surfaces at least 1⁄4 in. Self-furring lath meets furring requirements.
* Section 7.10.2.2 says ‘Staples shall have crowns not less than 3⁄4 in. (19.05 mm) and shall engage not less than three strands of lath and penetrate the wood framing members not less than 3⁄4 in.’
Cutting some slack for retrofit, what do you think?
All wrong. If chicken wire is used they will need furring nails that have the spacer. The other choice is to use self furring lathe that has the dimples. Both keep the wire the required 1/4 inch space.
The work is underway by a retried Union stuccoer… so making any suggestion something is wrong is very hard going. He has 30 years experience doing stucco.
Plus, the local building inspector passed this, so the code citation holds little weight (CBC 2510.3 specifies use of ASTM C 1063, which wants the 1/4" standoff, and the staples into the framing not the sheathing).
My opinion is he should have used the wire lath he used in the little spots everyware.
I have never used the chicken wire and do not see how it wold help hold the stucco in place???
Wire lath does have a top and bottom side and when installed top side up it helps hold the stucco in place. The small patches are patches and will definitely appear that way. Under the window may be ok but the hole patch should be stubnailed to the sides. It may work and MAY not crack but it may crack all around the circle hole.
The old stucco from 1950 obviously failed here. It was secured with roofing nails with the felt standoff into thin chicken wire. The wire rusted. The nails rusted. And the nails got loose.
Originally the building inspector wanted the stucco hammered to wire tie to the old chicken wire. But he conceded this was a fool’s errand after seeing this section:
30 years of doing it wrong and was never taught or learned how to do it right.
Man oh Man, look at this diaster zone.
Even the extension ladder is backwards.
The top flashing is a bit of a question also. That’s a foam roof up there, with the foam lapped over the parapet top. Tying into that is impossible, but maybe there’s a way to slip a flashing up to the parapet flashing (assuming there is a parapet flashing!)
Yes, this is in fact my very own house. The above looked wrong to me, so I delved into the details of ASTM C1063. The conversation with the general was difficult, because the stucco guy has so much experience, and a track record of flawless jobs (even if he’s doing it ‘wrong’).
Though note: the ladder is not in fact backwards. The area under the window is clearly not done. My concern is the details of the seaming, stapling, lathe, and flashing.
(I visited the badstucco website, but the photos are currently broken, and the email link does not work)…
Once a tradesman/crafstman puts the mud on the wall or cieling the lath/chicken wire is nothing more than rebar on a smaller scale.
A lot of what the experts bark about is over rated IMHO anyway.
the H stands for Humble.
A good stucco job will stand the test of time, it is the FAUX materials and things done to a structure before the stucco contractor gets there that causes a lot of failures these days.
Let alone the DUMBING down of the AMERICAN workforce in all trades.
No, neither new nor windows old has backer rod or sealant.
The old windows just had stucco mold to the trim and flat unpainted sills.
The flashing on the new windows is properly done (for example the rough opening slants outward and has a layer of flashing on it).
I don’t understand the point you’ve made.
House: 1938
Wall addition: 1953
The house was the site of non-disclosure by the selling Realtor (who handled the renovation). Here’s an example: note the brand new new 2x4’s and new door, on a wall that was then sealed caulked and painted shut: