Wind Mit Experts
After completing a ton of these wind Mits I finally get hit on a Re-Inspection. Been thru a Ton of them but never had this issue
Issue
The home is a 8 Million plus value home, company is Citizens. Upstairs there are Sonic Light tubes - Small 8" Tubes sealed units that go thru the roof and add light to the hallways. They are thick and heavy duty.
Whole house is Impact glass and I ignored the tubes as a Opening. They do not open.
Audit comes back with this is a Opening that is not rated. - Guys insurance goes up about 10K
So how do you solve this? No label on them and the attic is foamed in so can not get to the decking?
BY THE WAY I JUST GOT USE TO THE OLD FORM WHY DO WE ALWAYS SWITCH THIS FORM
When was the home built?
If it is newer, the records should be fairly easy to come by as far as permits, etc.
Find out the manufacturer and get something from them.
I suspect the other inspector is calling the tube a skylight.
Possibly these: tube lights
I have been waiting for this issue to hit. Unless the solar tube (skylight) has a Florida Product approval or NOA that demonstrates compliance with ASTM E 1886 and E 1996, then the opening would be unprotected per the guidelines on the wind mit form. Unfortunately, per the guidelines for the wind mit form, the “re-inspector” is likely correct- in this case. Unless of course, you can get the data for the solar tubes that demonstrate compliance with ASTM E 1886 and E 1996 and shove it down their throats.
Here you go, see Para 4b.
SECTION 08625
TUBULAR DAYLIGHTING DEVICE
Display hidden notes to specifier by using “File”/”Options”/”Display”/”Hidden Text”. For versions of Word prior to 2010 use: “Tools”/”Options”/“View”/”Hidden Text”.
**** NOTE TO SPECIFIER ** Solatube International, Inc.; residential and commercial tubular daylighting devices.**
This section is based on the products of Solatube International, Inc., which is located at:
** Solatube International**
** 2210 Oak Ridge Way**
** Vista, CA 92081-8341**
** Toll Free Tel: 888-765-2882 **
** Tel: (760) 477-1120 **
** Fax: (760) 597-4488**
** Email: **[email protected]
** Web: http://www.solatube.com](http://www.solatube.com/).
** [Click Here]](http://www.arcat.com/arcatcos/cos35/arc35591.cfm#http://www.arcat.com/arcatcos/cos35/arc35591.cfm) for additional information.
Solatube Daylighting Systems (DS) use advanced optics to significantly improve the way daylight is harnessed. Solatube International has added breakthrough technology throughout the system to capture more sunlight on the roof, transfer more sunlight through the tubing and effectively diffuse the light in the building interior. Solatube Daylighting Systems set performance standards never seen before. Highly effective and simple to install, these models can transform dark interior rooms and light more expansive spaces when used in multiples, creating a unique architectural effect.
Solatube Daylighting Systems can accommodate virtually any ceiling configuration including suspended ceilings, finished drywall ceilings, and open ceilings making them appropriate for a wide variety of commercial and residential applications, including office, retail, warehouse, industrial, education, healthcare facilities, multifamily housing, and custom homes. These Daylighting Systems provide significant energy savings, improved environments, and high-quality lighting.
PART 1 GENERAL
1.1 SECTION INCLUDES
A. Tubular daylighting device, consisting of roof dome, reflective tube, and diffuser assembly; configuration as indicated on the drawings.
**** NOTE TO SPECIFIER ** Delete the following paragraph if no daylight dimmers, security bars, light fixtures or ventilation accessories are specified.**
B. Accessories.
1.2 RELATED SECTIONS
**** NOTE TO SPECIFIER ** Delete any sections below not relevant to this project; add others as required.**
A. Section 07311 - Asphalt Shingles: Flashing of skylight base.
B. Section 07320 - Roof Tiles: Flashing of skylight base.
C. Section 07510 - Built-Up Bituminous Roofing: Flashing of skylight base.
D. Section 07530 - Electrometric Membrane Roofing: Flashing of skylight base.
E. Section 07550 - Modified Bituminous Membrane Roofing: Flashing of skylight base.
F. Section 07600 – Flashing: Metal flashings.
G. Section 08620 - Unit Skylights: Skylights without reflective tube.
H. Section 08630 - Metal Framed Skylights.
I. Section 15810 - Ducts: Fan vent duct and connections.
J. Section 16150 - Equipment Wiring: Electrical connections.
K. Section 16500 – Lighting Equipment and Controls: Light bulbs and lamps.
1.3 REFERENCES
**** NOTE TO SPECIFIER ** Delete references from the list below that are not actually required by the text of the edited section.**
A. ASTM B 209 - Standard Specification for Aluminum and Aluminum-Alloy Sheet and Plate.
B. ASTM E 84 - Standard Test Method for Surface Burning Characteristics of Building Materials; 2008a.
C. ASTM A 463/A 463M - Standard Specification for Steel Sheet, Aluminum Coated, by the Hot Dip Process; 2006.
D. ASTM A 653/A 653M - Standard Specification for Steel Sheet, Zinc Coated (Galvanized), by the Hot Dip Process; 2007.
E. ASTM E 283 - Test Method for Rate of Air Leakage Through Exterior Windows, Curtain Walls, and Doors Under Specified Pressure Differences Across the Specimen; 2004.
F. ASTM E 308 - Standard Practice for Computing the Colors of Objects by Using the CIE System; 2006.
G. ASTM E 330 - Structural Performance of Exterior Windows, Curtain Walls and Doors; 2002.
H. ASTM E 547 - Test Method for Water Penetration of Exterior Windows, Skylights, Doors and Curtain walls by Cyclic Air Pressure Difference; 2000.
I. ASTM E 1886 - Standard Test Method for Performance of Exterior Windows, Curtain Walls, Doors, and Impact Protective Systems Impacted by Missile(s) and Exposed to Cyclic Pressure Differentials.
J. ASTM E 1996 - Standard Specification for Performance of Exterior Windows, Curtain Walls, Doors, and Impact Protective Systems Impacted by Windborne Debris in Hurricane
K. ASTM D 635 - Test Method for Rate of Burning and/or Extent of Time of Burning of Self-Supporting Plastics in a Horizontal Position; 2006.
L. ASTM D-1929 - Test Method for Ignition Properties of Plastics; 1996 (2001).
M. UL 181 - Factory Made Air Ducts and Air Connectors
N. ICC AC-16 - Acceptance Criteria for Plastic Skylights; 2008.
O. Florida Building Code TAS 201 – Impact Test Procedures.
P. Florida Building Code TAS 202 – Criteria for Testing Impact and Non Impact Resistant Building Envelope Components Using Uniform Static Air Pressure Loading.
Q. Florida Building Code TAS 203 – Criteria for Testing Products Subject to Cyclic Wind Pressure Loading
1.4 PERFORMANCE REQUIREMENTS
A. Completed tubular daylighting device assemblies shall be capable of meeting the following performance requirements:
  1.     Air Infiltration Test: Air infiltration will not exceed 0.30 cfm/sf aperture with a pressure delta of 1.57 psf across the tube when tested in accordance with ASTM E 283.
  2.     Water Resistance Test: No uncontrolled water leakage at 10.5 psf pressure differential with water rate of 5 gallons/hour/sf when tested in accordance with ASTM E 547.
  3.     Uniform Load Test:
**** NOTE TO SPECIFIER ** Select the following Paragraph for use with Solatube Model 330 DS-O, 330 DS-C, 750 DS-O or 750 DS-C. Delete if not applicable.**
a. No breakage, permanent damage to fasteners, hardware parts, or damage to make daylighting system inoperable or cause excessive permanent deflection of any section when tested at a Positive Load of 150 psf (7.18 kPa) or Negative Load of 70 psf (3.35 kPa).
b. All units shall be tested with a safety factor of (3) for positive pressure and (2) for negative pressure, acting normal to plane of roof in accordance with ASTM E 330.
**** NOTE TO SPECIFIER ** Select the following Paragraphs for use with Solatube Models 750 DS-O and 750 DS-C with Polycarbonate Inner Dome Glazing or Models 290 DS and 160 DS with Acrylic Inner Dome Glazing. Delete if not applicable.**
4. Hurricane Resistance:
a. Meets Florida Building Code TAS, 201, TAS, 202 and TAS 203 for Impact and non-impact components.
b. Meets ASTM E 1886 and ASTM E1996 for missile and cyclic pressure differential testing.
5. Fire Testing:
a. When used with the Dome Edge Protection Band, all domes meet fire rating requirements as described in the 2006 International Building Code.
b. Self-Ignition Temperature - Greater than 650 degrees F per ASTM D-1929.
c. Smoke Density - Rating no greater than 450 per ASTM Standard E 84 in way intended for use. Classification C.
d. Rate of Burn and/or Extent - Maximum Burning Rate: 2.5 inches/min (62 mm/min) Classification CC-2 per ASTM D 635.
e. Rate of Burn and/or Extent - Maximum Burn Extent: 1 inch (25 mm) Classification CC-1 per ASTM D 635.
1.5 SUBMITTALS
A. Submit under provisions of Section 01300.
B. Product Data: Manufacturer’s data sheets on each product to be used, including:
  1.     Preparation instructions and recommendations.
  2.     Storage and handling requirements and recommendations.
  3.     Installation methods.
C. Shop Drawings. Submit shop drawings showing layout, profiles and product components, including anchorage, flashings and accessories.
D. Verification Samples: As requested by Architect.
E. Test Reports: Independent testing agency or evaluation service reports verifying compliance with specified performance requirements.
**** NOTE TO SPECIFIER ** Delete the following paragraphs if LEED is not applicable. Several opportunities exist for LEED credits when using daylighting systems specified. Contact Solatube International, Inc. for additional information.**
F. LEED Submittals: Provide documentation of how the requirements of Credit will be met:
  1.     List of Daylight Credits available for the products specified.
  2.     Data on Energy Optimization Performance Credits for the products specified.
  3.     Data on Regional Credits which may be available for the project location. (LEED 2.1)
  4.     Data on Perimeter and Non-Perimeter Controllability of Systems for use of Daylight Dimmer option with the products specified.
  5.     Data on potential Innovation in Design Credits which may be available for the innovative use of the products specified.
1.6 QUALITY ASSURANCE
A. Manufacturer Qualifications: Engaged in manufacture of tubular daylighting devices for minimum 15 years.
1.7 DELIVERY, STORAGE, AND HANDLING
A. Store products in manufacturer’s unopened packaging until ready for installation.
B. Store and dispose of solvent-based materials, and materials used with solvent-based materials, in accordance with requirements of local authorities having jurisdiction.
1.8 PROJECT CONDITIONS
A. Maintain environmental conditions (temperature, humidity, and ventilation) within limits recommended by manufacturer for optimum results. Do not install products under environmental conditions outside manufacturer’s absolute limits.
1.9 WARRANTY
A. Daylighting Device: Manufacturer’s standard warranty for 10 years.
**** NOTE TO SPECIFIER ** Delete if optional electric components are not required.**
B. Electrical Parts: Manufacturer’s standard warranty for 5 years, unless otherwise indicated.
PART 2 PRODUCTS
2.1 MANUFACTURERS
A. Acceptable Manufacturer: Solatube International, Inc.; 2210 Oak Ridge Way, Vista, CA 92081. ASD. Tel. Toll Free: 888-765-2882. Tel: (760) 477-1120. Fax: (760) 597-4488. Email: [email protected]. Web: www.solatube.com.
**** NOTE TO SPECIFIER ** Delete one of the following two paragraphs; coordinate with requirements of Division 1 section on product options and substitutions.**
B. Substitutions: Not permitted.
C. Requests for substitutions will be considered in accordance with provisions of Section 01600.
D. General Contractor will bear responsibility for costs associated with substitution review.
E. Requests for substitutions will be considered provided a lighting layout with photometric data is supplied to demonstrate light levels will meet original design intent.
2.2 TUBULAR DAYLIGHTING DEVICES
A. Tubular Daylighting Devices General : Transparent roof-mounted skylight dome and self-flashing curb, reflective tube, and ceiling level diffuser assembly, transferring sunlight to interior spaces; complying with ICC AC-16.
B. SolaMaster Series: Solatube Model 750 DS-C Penetrating Ceiling, 21 inch (530 mm) Daylighting System:
  1.     Roof Dome Assembly: Transparent, UV and impact resistant dome with flashing base supporting dome and top of tube.
a. Outer Dome Glazing: Type DA, 0.125 inch (3.2 mm) minimum thickness injection molded acrylic classified as CC2 material; UV inhibiting (100 percent UV C, 100 percent UV B and 98.5 percent UV A), impact modified acrylic blend.
b. Raybender 3000: Variable prism optic molded into outer dome to capture low angle sunlight and limit high angle sunlight.
**** NOTE TO SPECIFIER ** Select one of the following optional glazing paragraphs as required. CC1 Polycarbonate inner dome (Type DPI) meets Florida Building Code High Velocity Wind Zone requirements and Texas Department of Insurance Impact Resistant zone requirements. Delete the one not required. **
c. Inner Dome Glazing: Type DAI, 0.115 inch (3 mm) minimum thickness acrylic classified as CC2 material.
d. Inner Dome Glazing: Type DPI, 0.115 inch (3 mm) minimum thickness polycarbonate classified as CC1 material.
2. Roof Flashing Base:
**** NOTE TO SPECIFIER ** Select of the following flashing paragraphs and delete the one not required. Two piece is used on Standing Seam Rib metal roof profiles.**
a. One Piece: One piece, seamless, leak-proof flashing functioning as base support for dome and top of tube. Sheet steel, corrosion resistant conforming to ASTM A 653/A 653M or ASTM A 463/A 463M, 0.028 inch (0.7 mm) thick.
**** NOTE TO SPECIFIER ** Select one or more of the following flashing paragraphs and delete those not required. 8 inch or 11 inch bases are recommended for flat commercial roofs. Curb cap is normally used only on metal roofs or other roofs where curb is preferred and provided by others. **
  1.     Base Style: Type F4, Self mounted, 4 inches (102 mm) high.
  2.     Base Style: Type F8, Self mounted, 8 inches (203 mm) high.
  3.     Base Style: Type F11, Self mounted, 11 inches (279 mm) high.
  4.     Base Style: Type FC, Curb cap, with inside dimensions of 27 inches by 27 inches (685 mm x 685 mm) to cover curb as specified in Section 07600.
b. Two Piece: Two-piece, inverted flange Metal Roof Flashing for Standing Seam Rib roof profile with greater than 14-3/8 inch (365 mm) minimum distance between ribs permitting a required greater than 2 inch (51 mm) clearance between flashing and rib: Type FSM. Aluminum 1060 Alloy, corrosion resistant conforming to ASTM B 209, 0.059 inch (1.5mm) thick.
***** NOTE TO SPECIFIER ** The following flashing accessories are optional. Select those required and delete those not required. Flashing insulator is intended to seal the roof opening and prevent condensation forming on the flashing interior from exposure to humid air in unventilated spaces. **
3. Flashing Insulator: Type FI, Thermal isolation material for use under flashing.
**** NOTE TO SPECIFIER ** Select the following dome edge protection band paragraph when roof is fire rated with 8 inch high or less turret. Delete if not required.**
4. Dome Edge Protection Band: Type PB, For fire rated roofs with turret height less than 8 inches (203 mm). Galvanized steel. Nominal thickness of 0.039 inch (1 mm).
**** NOTE TO SPECIFIER ** The following turret extension accessories are optional. Select those required and delete those not required. If more than one size is required indicate locations on the Drawings.**
5. Roof Flashing Turret Extensions: Provide manufacturer’s standard extensions for applications as requiring:
a. Type T12: Additional lengths of 12 inches (300 mm) extension.
b. Type T24: Additional lengths of 24 inches (600 mm) extension.
c. Type T36: Additional lengths of 36 inches (900 mm) extension.
d. Type T48: Additional lengths of 48 inches (1200 mm) extension.
6. Tube Ring: Attached to top of base section; 0.090 inch (2.3 mm) nominal thickness injection molded high impact PVC; to prevent thermal bridging between base flashing and tubing and channel condensed moisture out of tubing.
7. Dome Seal: Adhesive backed weatherstrip 0.63 inch (16 mm) tall by 0.28 inch (7 mm).
8. Reflective Tubes: Aluminum sheet, thickness 0.018 inch (0.5 mm).
a. General:
  1.     Interior Finish: Spectralight Infinity high reflectance specular finish on exposed reflective surface. Specular reflectance for visible spectrum (400 nm to 760 nm) greater than 99 percent.  Total solar spectrum reflectance (400 nm to 2500 nm) less than 80.2 percent.
  2.     Color: a* and b* (defined by CIE L*a*b* color model) shall not exceed plus 2 or be less than minus 2 as determined in accordance to ASTM E 308.
**** NOTE TO SPECIFIER ** Select the following optional Extension Tube and Angle Adapters as required. Delete if not required. Note that at least one Bottom Tube Angle Adapter is required for transition box.**
b. Top Tube Angle Adapter, Type TA:
  1.     Reflective 45 degree adjustable Top Tube Angle Adapter, 16 inches (406 mm) long.
c. Bottom Tube Angle Adapter, Type BA:
  1.     Reflective 45 degree adjustable Bottom Tube Angle Adapter, 16 inches (406 mm) long, required for transition box.
d. Top Tube Angle Adapter and Bottom Top Tube Angle Adapter Kit, Type AK:
  1.     Reflective 45 degree adjustable top and bottom angle adapters (one each), 16 inches (406 mm) long
e. Extension Tube:
  1.     Reflective extension tube, Type EXX, Notched for Open Ceiling diffuser attachment, 24 inches (610 mm) long
f. Reflective 90 degree Adjustable tube:
  1.     Extension Tube Angle Adapter: Provide manufacturer's standard adapters for applications requiring:
(a) Type A1 one 0 to 90 degree extension tube angle adapter.
(b) Type A2 two 0 to 90 degree extension tube angle adapters.
9. Diffuser Assemblies for Tubes Penetrating Ceilings: Solatube Model 750 DS-C. Ceiling mounted box transitioning from round tube to square ceiling assembly, supporting light transmitting surface at bottom termination of tube; 23.8 inches by 23.8 inches (605 mm by 605 mm) square frame to fit standard suspended ceiling grids or hard ceilings.
a. Round to square transition box made of opaque polymeric material, classified as CC2, Class C, 0.110 inch (2.8 mm) thick.
**** NOTE TO SPECIFIER ** Select one of the following lens paragraphs and delete the one not required.**
b. Lens: Type L1 OptiView Fresnel lens design to maximize light output and diffusion with extruded aluminum frame and EPDM foam seal to minimize condensation and bug, dirt and air infiltration per ASTM E 283. Visible Light Transmission shall be greater than 90 percent at 0.022 inch (0.6 mm) thick. Classified as CC2.
c. Lens: Type L2 Prismatic lens design to maximize light output and diffusion with extruded aluminum frame and EPDM foam seal to minimize condensation and bug, dirt and air infiltration per ASTM E 283. Visible Light Transmission shall be greater than 90 percent at 0.100 inches (2.5 mm) thick. Classified as CC2.
**** NOTE TO SPECIFIER ** Select the following optional lens paragraphs and delete if not required. Required for energy star rating. Supplemental Natural Effect Lens is also required to meet Florida Building Code High Velocity Wind Zone and Texas Department of Insurance Impact Resistant zone requirements.**
d. Supplemental Natural Effect Lens made of acrylic, classified as CC2, Class C, 0.060 inch (1.5 mm) thick, with open cell foam seal to minimize condensation and bug, dirt and air infiltration per ASTM E 283.
**** NOTE TO SPECIFIER ** The following accessories are optional. Select those required and delete those not required.**
10. Accessories:
a. Security Bar: Type B Security Bar 0.375 inch (95 mm) stainless steel bar across flashing diameter opening.
b. Wire Suspension Kit: Type E, Use the wire suspension kit when additional bracing to the structure is required.
c. Local Dimmer Control utilizing a butterfly baffle design of Spectralight Infinity reflective material to minimize shadowing when in use: Provided with dimmer switch and cable.
  1.     Daylight Dimmer: Type D Electro-mechanically actuated daylight valve; for universal input voltages ranging between 90 and 277 V at 50 or 60 Hz; maximum current draw of 50 ma per unit; controlled by low voltage, series Type T02: circuited, 4 conductor, size 22 cable; providing daylight output between 2 and 100 percent. Provided with dimmer switch and cable.
  2.     Switch: Type SW, Manufacturer-specific low voltage DC DP/DT switch (white) required to operate Daylight Dimmer.  Note: only one switch is required per set of synchronously controlled dimmers.
  3.     Cable: Type CA, Two conductor low voltage cable (500 foot) for multiple unit DC connection.
**** NOTE TO SPECIFIER ** The following accessory is only available when an Inner Dome option is selected (Type DAI or Type DPI).**
d. Security Kit: Type SK Dome Security Kit, rivets with nylon spacers to replace dome screws.
2.3 ACCESSORIES
A. Fasteners: Same material as metals being fastened, non-magnetic steel, non-corrosive metal of type recommended by manufacturer, or injection molded nylon.
B. Suspension Wire: Steel, annealed, galvanized finish, size and type for application and ceiling system requirement.
C. Sealant: Polyurethane or copolymer based elastomeric sealant as provided or recommended by manufacturer.
PART 3 EXECUTION
3.1 EXAMINATION
A. Do not begin installation until substrates have been properly prepared.
B. If substrate preparation is the responsibility of another installer, notify Architect of unsatisfactory preparation before proceeding.
3.2 PREPARATION
A. Clean surfaces thoroughly prior to installation.
B. Prepare surfaces using the methods recommended by the manufacturer for achieving the best result for the substrate under the project conditions.
3.3 INSTALLATION
A. Install in accordance with manufacturer’s printed instructions.
B. After installation of first unit, field test to determine adequacy of installation. Conduct water test in presence of Owner, Architect, or Contractor, or their designated representative. Correct if needed before proceeding with installation of subsequent units.
3.4 PROTECTION
A. Protect installed products until completion of project.
B. Touch-up, repair or replace damaged products before Substantial Completion.
END OF SECTION
Meets ASTM 86 and 96. Tell that to the Inspection Depot lackey!
Let us know how it turns out.
All you have to do now is prove that these are the ones.
After looking around, it is my understanding that all of these tube lights meet the standards required. Or, more precisely, there are models in each manufacturers line that meet the standards. All you have to do now is prove it.
After you do, make sure you remind your client that you were right and a small donation for saving him 10K may be in order…after all it is the Christmas Season!
Good luck!
here is the part you need which was cut off
SECTION 08625
PART 1 GENERAL
B. Accessories.
1.3 REFERENCES
Sorry, Eric, I was posting the same thing as you!
Openings do not have to open(skylights) to require protection. The inspector has the burden of proving the opening protection.
It does not matter what the inspector believes it matter what can be proven. If you know the manufacturer submit the proper paperwork and be done.
Check the roof permit date. If the roof was permited to the 2001 building code, NOA’s for the skylights should be part of that permit application. Contact Building Dept. and see if the have documentation as to skylights installed.
those are easy to find with roof docs
If you cannot find the info…seems like adding a panel to cover this that is Miami Dade approved would be easy…
Or, since they appear to be relatively inexpensive, replace them with compliant ones.
Or, just call the company and tell them you need new stickers…:mrgreen: :mrgreen:
Add, “label maker” to the recommended homeowner tool kit
The opening does not have to open to be considered. In this situation the roof permit may be the only way to determine if they are rated. I have had homeowners give me an noa supplied by the roofer but yet skylights are not listed on the permit and there is no way to prove that noa is for that skylight. You must have proof.
How many guys have been able to call a skylight rated by verifying on site with no other documentation like a permit?
newer skylights are usually labeled. There are only a couple manufacturers
even the rated tubes are usually etched inside the glass, hard to see…but there
Like you said Dennis, the etching is very hard to see. Im just curious on how many guys are calling them rated without even having a clue if the are our not. We inspect every house that a local roofer reroofs and all skylights are on the permit and most of the time that is the only way to verify.
Yeah, take THAT photo! All the sonotubes are impact resistant 1/4" plexi the reinspector is WRONG tell the homeowner to institute a lawsuit for fraud against the insurance company and the inspector. Just make sure you are right first.
im with ya
usually when it says miami dade county approved with the manufacture’s name… Its a slam dunk. Otherwise, you need docs