Help with an Electrical Panel

Originally Posted By: mgault
This post was automatically imported from our archived forum.



http://www.nachi.org/bbsystem/usrimages/0/050818053312.JPG ]


Second shows 'bunched' nuetrals and grounds into the bar. ![icon_eek.gif](upload://yuxgmvDDEGIQPAyP9sRnK0D0CCY.gif)

[ Image: http://www.nachi.org/bbsystem/usrimages/0/050818053304.JPG ]


Tried to get a third in (is there a limit?)

Ah here it is.
Nicely detailed "note book" paper to id the Breaker assignments..

[ Image: http://www.nachi.org/bbsystem/usrimages/0/0508180529361.JPG ]


Appreciate any help!


--
-Mike
A to Z Home Inspections, LLC

www.atozhomeinspections.net

Originally Posted By: Joey D’Adamo
This post was automatically imported from our archived forum.



Those pigtails are likely okay.


Originally Posted By: jpope
This post was automatically imported from our archived forum.



No problem with the wire nuts.


Neutrals are current carrying conductors. Current carrying conductors require individual terminations (as of 2002).

Grounds and neutrals were never allowed to share the same terminal connection as far as I know.


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: mgault
This post was automatically imported from our archived forum.



The wire nuts appeared to “extend” several neutrals from the bottom of the panel up to the areas where they were ‘bunched’ into the common bar.


Is that okay too?


--
-Mike
A to Z Home Inspections, LLC

www.atozhomeinspections.net

Originally Posted By: lkage
This post was automatically imported from our archived forum.



mgault wrote:
The wire nuts appeared to "extend" several neutrals from the bottom of the panel up to the areas where they were 'bunched' into the common bar.

Is that okay too?




Grounded conductors (neutrals) need their own termination. One per lug screw.


--
"I have never met a man so ignorant that I couldn't learn something from him."
Galileo Galilei

Originally Posted By: lgoodman
This post was automatically imported from our archived forum.



They have already answered your first two questions. Wire nut on neutral o.k. If the wire is too short to reach I know of no other practical solution.


One neutral per screw. Grounds may be ganged.

Notebook paper directory. Give the man extra credit. Many electricians won't even use the factory provided sticker or they provide minimal, confusing and incomplete information. Can't be too much info for me. I carry a Sharpie and write on junction box covers and leave all kinds of notes for whoever may come along after me. You could advise the client to have the electrician who makes repairs also make the directory more permanent.


Originally Posted By: mgault
This post was automatically imported from our archived forum.



of that?



-Mike


A to Z Home Inspections, LLC


www.atozhomeinspections.net

Originally Posted By: lkage
This post was automatically imported from our archived forum.



lgoodman wrote:
Grounds may be ganged.


I believe it's:

(2) 14 or 12 CU per lug screw
or
(2) 12 or 10 AL per lug screw


--
"I have never met a man so ignorant that I couldn't learn something from him."
Galileo Galilei

Originally Posted By: mgault
This post was automatically imported from our archived forum.



I wrote it all up…


In for a penny, in for a pound (mixed metaphor or British origin? ![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif) )


--
-Mike
A to Z Home Inspections, LLC

www.atozhomeinspections.net

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



I agree with Leigh. A notebook paper directory that is right is a lot better than the factory sheet that is wrong.