Is there a height requirement for the meter. Ihave read 4 feet in the past but I can’t find a code reference. I think this one was probably fine before the deck was added. Also, who would fix this? an certified, qualified, licensed awesome master electrician :mrgreen: or the utility company?
1 If your electric meter will be
under it, the deck must be at
least 7 feet high.
2 There must be 36 inches of
unobstructed space in front of
the meter.
3 There must be a 36-inch
wide unobstructed travel path in
front of the meter.
4 There must be at least
2 inches of space on both sides
of the meter.
5 No structure may be built
around the meter, except for
approved meter rooms.
6 Doors or windows cannot be
within one foot of the meter.
7 Meters located inside fenced
areas must have gate access.
Interesting checklist…not sure of it’s correctness but to each his own. I would also check to see the deck had a permit pulled as it obviously came after the meter was installed.
Also just some FYI…section 230.66 says that meter enclosures are not considered part of service equipment. Installed by the electrician and typically once sealed property of utility.
At the end of the day the biggest concern for me would be if the deck had permits. Guidelines are great but not law. Fact is will this meter enclosure need servicing, maintenance and so on…most likely not. Now, the POCO may have a concern but again thats not a defect u would flame out.
I advice to mention it in the report as something to be aware of and to watch out fir but other than that no serious concern…to me anyway in my opinion and in a buyers prospective opinion. How many completed meter enclosures you been into???probably none after the origional installation.