Split strands

Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



Anyone ever see someone split the strands of a ground wire to make them fit in a busbar?






Wisconsin Home Inspection, ABC Home Inspection LLC


Search the directory for a Wisconsin Home Inspector

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Yes, and it is not code compliant.



Bob (AKA iwire)


ECN Discussion Forums


Mike Holt Code Forum

Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



Bob Badger wrote:
Yes, and it is not code compliant.


Why? What would be the downside?


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Downside.


Not code compliant.

To answer what I think you mean---nothing.

Mike P.


Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Also note that multi feed to breaker 3 & 5 are on the same leg.


Mike P.


Originally Posted By: jpeck
This post was automatically imported from our archived forum.



The downside would be that one ‘set’ of the strands could come loose in its terminal, providing an inadequate grounding path for that size conductor through the remaining strands in the other terminal should the need for this grounding path arise.


Also, I am sure you noticed, neutral and grounds in the same terminal, multiple tapped breaker (looks like it anyway).


--
Jerry Peck
South Florida

Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



Not sure what you meant by the remark on 3 and 5…#4 has a double tapped breaker, which was noted.


I think the view is skewed and you are seeing shadows of wires for the neutral/grounded connex from the flash and light near the panel. They were each in seperate terminals. Lots of homeowner wiring in this home…lots of “evaluate by a licensed electrician” remarks in the report.



Wisconsin Home Inspection, ABC Home Inspection LLC


Search the directory for a Wisconsin Home Inspector

Originally Posted By: tallen
This post was automatically imported from our archived forum.



I believe that is breaker #8


breakers are # as follows or I could be wrong.


1,2
3,4
5,6
7,8
9,10
etc.


--
I have put the past behind me,
where , however, it now sits, making rude remarks.

www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Quote:

Plant Engineering's Arc Flash Webcast, sponsored by Schneider Electric/Square D, DuPont, AVO Training Institute, and ESA.

The webcast will be archived at plantengineering.com until July 8, 2004. Use
the following link to launch the presentation from April 8:

http://web1.media.globix.net/client/planteng/040804/launch.htm

Plant Engineering Magazine



--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Mike Parks
This post was automatically imported from our archived forum.



Thanxs.


Kind of hard for me to point something out when I do not know which side of the panel that I am on. ![icon_redface.gif](upload://f7DX2EWhmUfsDapWaYT3oJHMCj1.gif)

I meant #6 & #8.

Mike P.


Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



[quote=“jpeck”]The downside would be that one ‘set’ of the strands could come loose in its terminal, providing an inadequate grounding path for that size conductor through the remaining strands in the other terminal should the need for this grounding path arise.quote]


Jerry, Isn't it more likely that one terminal could come loose than two? If all the strands are under one terminal (as they should be) and that one comes loose you have zero protection. But if the strands are split to two different terminals and one comes loose, atleast you have protection up to the capacity of the remaining intact wires. Isn't some better than none?

Also wouldn't the total surface contact area between the terminal bar and the grounding wire be greater if they are split, resulting in a cooler (not this ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif) kind of cooler ) connection

I don't really see why its a problem. What am I missing?


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Paul,


Would you accept seeing feeder conductors with some strands cut off so that a larger size conductor will fit into a too small terminal?

How about if those other strands were not cut off, but were installed in another lug? Would you accept that?

Please explain your yes or no, then I will know how to explain the ground problem to you.


--
Jerry Peck
South Florida

Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



Quote:
How about if those other strands were not cut off, but were installed in another lug?

I have never seen a residential panel with more than one spot per leg for a feeder wire. So I would question it. Also I would be concerned about the exposure of uninsulated wire that there would need to be in order to separate strands in the service entrance wires. Something that does not apply to the grounding wire scenario.


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



phinsperger wrote:
If strands are cut off feeder then the total capacity of the wire is reduced. I would not accept that.


I agree with that.

phinsperger wrote:
Also I would be concerned about the exposure of uninsulated wire that there would need to be in order to separate strands in the service entrance wires. Something that does not apply to the grounding wire scenario.


But would you be concerned about the conductor being in two separate terminals?


--
Jerry Peck
South Florida

Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



Jerry,


That in its self would not concern me. What would concern me is;

1) Was the panel modified to this configuration
2) Lack of proper insulation up to the lugs
3) Strands not secured in any lug or missing completely

The issue of strands separated and secured into two separated but connected lugs would not concern me.

We are talking about something like this;
![](upload://moO4lKSselGlXnrSzoyXYVD8aw3.jpeg)


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



phinsperger wrote:
The issue of strands separated and secured into two separated but connected lugs would not concern me.


It does concern me. I will, and do, write them up.


--
Jerry Peck
South Florida

Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



be unknowns or is there a concrete reason? Haven’t actually come accross one yet. Sounds like you have. So what else are seeing that I’m just not getting.


Like I said, I think that the overall connection would be cooler due to the increased surface area of contact.

Joe T., do what do you think about all this?


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



I agreed with Bob Badger and I agree with you. I will add more later as to why.



Joe Tedesco, NEC Consultant


www.nachi.org/tedescobook.htm

Originally Posted By: jpeck
This post was automatically imported from our archived forum.



Paul,


I've seen this a few times, and one terminal is always loose, meaning the conductor size is now reduced by the number of strands in the loose terminal. Sometimes, you will have two loose terminals.

This is because they are trying to fit a too large conductor into too small of a terminal. When they split the conductor strands, they do so with as short of a section as possible, and try to cram and bend from one terminal to another, with the conductor sets of strands (one or both sets) going into the terminal at an angle and not allowing the terminal screw to be properly tightened down on the conductor.

I've never seen any good come from this.


--
Jerry Peck
South Florida

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



There a lot of things that you can do in the electrical trade that will work, but are still violations of the code, occasionally there may be no direct answer to why we can not do something.


Splitting the strands is a often used short cut, I would be willing to bet there are tens of thousands of panels in the US that have split strands, just like there are many thousands of double tapped breakers.

Almost never will either cause problems.

But they are violations and they should tip off anyone looking at this work that the installer does not know or respect the code.

It could also indicate a disregard for safety and professionalism.

You want a reason this could be failed by am electrical inspector?

110.3(B)

The terminal is listed for a certain size maximum conductor.

Splitting a conductor does not change the size of the conductor.

A conductor that was manufactured and listed as 4 AWG can not be converted in the field to become two 8 AWG conductors.

With the strands split there is also a violation of 310.4, conductors in parallel.

Is this being picky?

I do not think so, I can not pick and choose which code rules I want to follow.

All that said, they make a very inexpensive device to connect lager conductors on these types of terminal bars.

A professional would use one.

I will step off the soap[ box now. ![icon_rolleyes.gif](upload://iqxt7ABYC2TEBomNkCmZARIrQr6.gif)

Bob


--
Bob (AKA iwire)