Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.
There a lot of things that you can do in the electrical trade that will work, but are still violations of the code, occasionally there may be no direct answer to why we can not do something.
Splitting the strands is a often used short cut, I would be willing to bet there are tens of thousands of panels in the US that have split strands, just like there are many thousands of double tapped breakers.
Almost never will either cause problems.
But they are violations and they should tip off anyone looking at this work that the installer does not know or respect the code.
It could also indicate a disregard for safety and professionalism.
You want a reason this could be failed by am electrical inspector?
110.3(B)
The terminal is listed for a certain size maximum conductor.
Splitting a conductor does not change the size of the conductor.
A conductor that was manufactured and listed as 4 AWG can not be converted in the field to become two 8 AWG conductors.
With the strands split there is also a violation of 310.4, conductors in parallel.
Is this being picky?
I do not think so, I can not pick and choose which code rules I want to follow.
All that said, they make a very inexpensive device to connect lager conductors on these types of terminal bars.
A professional would use one.
I will step off the soap[ box now. 
Bob
--
Bob (AKA iwire)