  • Where must gas shutoff valves be located? Where must appliance shutoff valves be installed? Equipment shutoff valves for a fireplace?
G2420.5 (409.5) Appliance shutoff valve
Located within same room.
The shutoff valve shall be located in the same room as the appliance. The shutoff valve shall be within 6 feet (1829 mm) of the appliance, and shall be installed upstream of the union, connector or quick disconnect device it serves. Such shutoff valves shall be provided with access. Appliance shutoff valves located in the firebox of a fireplace shall be installed in accordance with the appliance manufacturer’s instructions.
In reference to Writing Assignment #6, 2021 IRC Exam Study Course: R502.8.1
Notches in solid lumber joists, rafters and beams shall not exceed one-sixth of the depth of the member, shall not be longer than one-third of the depth of the member and shall not be located in the middle one-third of the span. Notches at the ends of the member shall not exceed one-fourth the depth of the member. The tension side of members 4 inches (102 mm) or greater in nominal thickness shall not be notched except at the ends of the members. The diameter of holes bored or cut into members shall not exceed one-third the depth of the member. Holes shall not be closer than 2 inches (51 mm) to the top or bottom of the member, or to any other hole located in the member. Where the member is also notched, the hole shall not be closer than 2 inches (51 mm) to the notch.
Wood sill plates and wood walls supported directly on continuous foundations shall be anchored to the foundation in accordance. with section R403.1.6 . 1/2 inch - diameter anchor bolts spaced no greater than 6 feet on center. Bolts shall extend a minimum of 7 inches into concrete.
  • How are trusses to be connected to the wall plates to address uplift pressures?
To address uplift pressures, trusses are typically connected to wall plates using hurricane ties or seismic ties. These metal connectors are secured with appropriate fasteners to provide a strong and resistant connection, helping to prevent truss uplift during high winds or seismic events.
  • At what minimum height is a masonry chimney required to terminate?
A masonry chimney must extend at least 3 feet above the highest point where it passes through the roof and be at least 2 feet higher than any portion of the building within a 10-foot horizontal distance.
  • How high above a floor in a garage is an appliance with an ignition source required to be located?
In a residential garage, appliances with an ignition source, such as a gas water heater or furnace, are generally required to be elevated at least 18 inches above the floor. This elevation helps reduce the risk of flammable materials, like gasoline or other combustibles, coming into contact with the appliance’s ignition source, enhancing safety.
In reference to writing assignment #7, 2021 IRC Exam Study Course: A minimum 0.019-inch (0.5 mm) (No. 26 galvanized sheet gage), corrosion-resistant weep screed or plastic weep screed, with a minimum vertical attachment flange of 3½ inches (89 mm), shall be provided at or below the foundation plate line on exterior stud walls in accordance with ASTM C926. The weep screed shall be placed not less than 4 inches (102 mm) above the earth or 2 inches (51 mm) above paved areas and shall be of a type that will allow trapped water to drain to the exterior of the building. The weather-resistant barrier shall lap the attachment flange. The exterior lath shall cover and terminate on the attachment flange of the weep screed.
In reference to writing assignment #8, 2021 IRC Exam Study Course: Installation of asphalt shingles shall abide with the IRC R905.2.1 section. Only on roofs of two units vertical in 12 units horizontal (2:12) or greater. For roof slopes from two units vertical in 12 units horizontal (2:12) and less than four units vertical in 12 units horizontal (4:12), double underlayment application is required in accordance with section 905.1.1. Asphalt shingles shall comply with ASTM D3462
Concrete slab on ground floors shall be designed and constructed in accordance with section 506 or ACI 322. Floors shall be a minimum 3 1/2 inches thick (for expansive soils. See section R403.1.8. The specified compressive strength of concrete shall be as set forth in section R402.2
  • Where must mechanical exhaust air terminate? What locations are strictly prohibited?
exhaust air should be terminated outdoors to ensure that contaminants and odors are not recirculated into indoor spaces. This may involve venting the air to the atmosphere or outside the building.
Mechanical exhaust air should not be discharged(within 3feet) near fresh air intake locations, as this could lead to the recirculation of contaminants into the building’s ventilation system.
In reference to writing assignment #9, 2021 IRC Exam Study Course: Masonry over a fireplace opening shall be supported by a lintel of noncombustible material. The minimum required bearing length on each end of the fireplace opening shall be 4 inches (102 mm). The fireplace throat or damper shall be located not less than 8 inches (203 mm) above the lintel. Footings for masonry fireplaces and their chimneys shall be constructed of concrete or solid
masonry not less than 12 inches (305 mm) thick and shall extend not less than 6 inches (152
mm) beyond the face of the fireplace or foundation wall on all sides. Footings shall be founded
on natural, undisturbed earth or engineered fill below frost depth. In areas not subjected to
freezing, footings shall be not less than 12 inches (305 mm) below finished grade.
The interior stairway requires illumination. The illumination level must be 1 1-foot candle (dull light) measured at the center of the treads and landing. There must be an on/off switch located at the upper and lower landing for stairways with 6 or more risers.
Exterior stairways must provide illumination at the top landing for a stairway going up from the ground surface and at the bottom landing for stairways going down from the ground surface.
General vs Specific requirements of the IRC
Specific requirements are always required to be applied to the standard in question. If there are no specific requirements for the application general requirements may be followed.
In reference to writing assignment #11, 2021 IRC Exam Study Course: M1602.2 Return air openings for heating, ventilation and air-conditioning systems shall comply with all of the following:
  1. 1.Openings shall not be located less than 10 feet (3048 mm) measured in any direction from an open combustion chamber or draft hood of another appliance located in the same room or space.
  2. 2.The amount of return air taken from any room or space shall be not greater than the flow rate of supply air delivered to such room or space.
  3. 3.Return and transfer openings shall be sized in accordance with the appliance or equipment manufacturer’s installation instructions, Manual D or the design of the registered design professional.
  4. 4.Return air shall not be taken from a closet, bathroom, toilet room, kitchen, garage, mechanical room, boiler room, furnace room or unconditioned attic.
Exceptions:
  1. 1.Taking return air from a kitchen is not prohibited where such return air openings serve the kitchen only, and are located not less than 10 feet (3048 mm) from the cooking appliances.
  2. 2.Dedicated forced-air systems serving only the garage shall not be prohibited from obtaining return air from the garage.
  3. 5.For other than dedicated HVAC systems, return air shall not be taken from indoor swimming pool enclosures and associated deck areas except where the air in such spaces is dehumidified,
  4. 6.Taking return air from an unconditioned crawl space shall not be accomplished through a direct connection to the return side of a forced-air furnace. Transfer openings in the crawl space enclosure shall not be prohibited.
  5. 7.Return air from one dwelling unit shall not be discharged into another dwelling unit.
Where are smoke alarms required to be located? Do they need to be interconnected? How must they be powered? What must be done when alterations or repairs take place?
Smoke detectors are to be installed in each sleeping room and outside each sleeping area. Smoke detectors are to be installed on each additional story of the home including basements and habitable attics. In split-level homes, without an intervening door between levels, the smoke detector on the upper floor shall be sufficient as long as the lower floor is less than one full story below the upper level.
Smoke alarm systems shall be installed so that when one smoke alarm is activated all smoke alarms respond and sound an alarm. This interconnectedness can be accomplished through hard wiring between all detectors or through wireless Bluetooth connection between units.
In reference to writing assignment #12, 2021 IRC Exam Study Course: Vents for natural draft appliances shall terminate not less than 5 feet (1524 mm) above the highest connected appliance outlet, and natural draft gas vents serving wall furnaces shall terminate at an elevation not less than 12 feet (3658 mm) above the bottom of the furnace. m1804.2.3
In reference to writing assignment #2, 2021 IRC Exam Study Course: Combustible insulation shall be separated not less than 3 inches from recessed luminaires, fan motors and other heat producing devices, with the exception where heat producing devices are listed for lesser clearances.
The definition of Light-frame construction is: Construction whose vertical and horizontal structural elements are formed by a system of repetitive wood or cold formed steel framing members.
In reference to Writing Assignment #13, 2021 IRC Exam Study Course:
Appliances shall not be located in sleeping rooms, bathrooms, toilet rooms, storage closets or surgical rooms, or in a space that opens only into such rooms or spaces , except where the installation complies with exemptions. G2406.2 (303.3)Prohibited locations & Exemptions
In reference to Writing assignment #3, 2021 IRC Exam Study Course:
Escape and rescue openings are required in Basements, habitable attics, and every sleeping room shall have not less than one operable emergency escape and rescue opening. Emergency escape and rescue shall have a net clear opening of not less than 5.7 square feet, where a window is provided as the emergency escape and rescue opening, it shall have a sill height of not more than 44 inches.