Two Mains

Originally Posted By: berby
This post was automatically imported from our archived forum.



http://www.nachi.org/bbsystem/usrimages/N/NACHI_001.jpg ]


Originally Posted By: jpope
This post was automatically imported from our archived forum.



removed the dead front cover, it looks okay.


But what's up with the EMT that appears to be tapped in before the meter? Again, I am assuming this is a lateral not a drop.


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



Jeff’s right again…if the house had two mains, it would have two meters…I see that quite often.



Wisconsin Home Inspection, ABC Home Inspection LLC


Search the directory for a Wisconsin Home Inspector

Originally Posted By: berby
This post was automatically imported from our archived forum.



Thanks Guys.


Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Barron,


Who's Rig are you standing in front of, in your avatar?

Jeff,

That EMT is protecting a ground wire going to a ground rod.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: jpope
This post was automatically imported from our archived forum.



dvalley wrote:
Jeff,

That EMT is protecting a ground wire going to a ground rod.


Ah ha.


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



dvalley wrote:
Barron,

Who's Rig are you standing in front of, in your avatar?

Jeff,

That EMT is protecting a ground wire going to a ground rod.


That's what I was thinking...but you can't really tell without opening up the disconnect panel at the meter.


--
Wisconsin Home Inspection, ABC Home Inspection LLC

Search the directory for a Wisconsin Home Inspector

Originally Posted By: pabernathy
This post was automatically imported from our archived forum.



probably just a crude method for obtaining a 400A service…most meter bases of that size allow (2) terminal points per phase on the contact area. We do it all the time for 400A services…with (2) 200A panels side by side but we do this inside and not on the outside wall…



Paul W. Abernathy- NACHI Certified


Electrical Service Specialists


Licensed Master Electrician


Electrical Contractor


President of NACHI Central Virginia Chapter


NEC Instructor


Moderator @ Doityourself.com


Visit our website- www.electrical-ess.com

Originally Posted By: bking
This post was automatically imported from our archived forum.



Paul,


What is the correct terminology here? I understand that even though residential service has two 120v feeds that are of a different phase, the correct terminology is 120/240 single phase service. I have seen it also written that there is no such thing as two phase service. It seems that electricians are the most likely to refer to it as two phase.

thanks for info


--
www.BAKingHomeInspections.com

Originally Posted By: bking
This post was automatically imported from our archived forum.



Kevin,


You can have two service equipment panels with just one meter.

A 400amp meter base with two 200A service equip panels in parallel each feeding two 200A interior load side panels.


--
www.BAKingHomeInspections.com

Originally Posted By: pabernathy
This post was automatically imported from our archived forum.



First, a ?phase? is a coil of wire in a transformer. When we use the term, we normally mean the voltage (Electrical Pressure) and current (electrons moving) across that coil. Most residences have single phase power as an electrical service to that structure. That means that 240 Volts is supplied to the building. In an attempt to make that safer, they take the center of that coil and ?Ground? it. Making the center of that coil the same electrical potential as the earth or floor we typically stand on, by attaching a conductor (wire) from the electrical and physical center of the winding to the earth, by a rod driven into the earth, hence ?Grounded.


Alternating current is an electrical potential with constantly changing amplitude and a periodically changing direction. That means that the electrical potential across the phase moves in one direction for 1/120th of a second, then stops and returns in the other direction for the next 1/120th of a second. The amplitude in the definition refers to the strength of electrical pressure or Voltage as that potential rises from zero (None) to a positive peak. Then the strength of electrical pressure falls through zero, to a negative peak, then again, through zero to a positive peak and repeats that process.

We call one cycle, the time (Period) it takes to move from one point and direction of amplitude through one peak, say positive, then through the other peak, say negative, then back to the original point (being in the same electrical direction). When the time for 360 electrical degrees, or one complete cycle, takes 16 2/3 thousandths of a second, then we call that 60 Cycles per Second or simply 60 Hertz (Hz).

In any phase the difference of electrical potential between one end of the coil and the other is 180 electrical degrees, much like the dry cell (battery) in your flashlight. If one end is positive, the other end has to be negative. An Alternating Current, unlike the battery is constantly changing.

With Three-Phase, you have three coils of wire in a transformer. Each phase (coil of wire) acts exactly as mentioned earlier. They are however, spaced, relative to time, 120 Electrical Degrees apart. That is likened to three guys all standing around the same tent peg, each taking a turn at striking the peg to drive it into the ground. Each guy is operated at 60 Hz, so the time one guy strikes the peg is every 16 2/3 thousandths of a second. Where relative to time, each guy is 120 Electrical degrees apart and before the first guy hits the tent peg a second time, the other two guys have already struck the peg. Three guys striking the peg can put the tent peg to depth in 1/3rd the time that one guy can put it in.

If it is not important to you to have the peg in faster, you can use smaller guys, or smaller mallets. This opens the door to understand the pros and cons of single-phase and three phase benefits or compromises.

First thing, your Kilowatt-Hour usage is the same, because it measures work. The work (tent peg) does not care if you have single-phase (one big guy with big mallet) or three-phase (three smaller guys with smaller mallets). It is the same work being accomplished. Your electric utility has different rates, where they charge for demand (Big slugs of current needed and for how long), KVAR Hour (Is the current moving when the voltage tells it to, or is it slightly different) and other considerations effecting the cost of those kilowatts.

If your load is under 48,000 Watts or 48KW, then Single-Phase is most likely cheaper, because of how the Electric Utility is likely to bill those kilowatts. If you are starting large motors and your load is above 35KW, then Three-Phase is likely to be cheaper. That being said, let?s investigate other costs.

A larger conductor (wire) allows more electrons to pass, enabling more work to be done. Larger wire is more copper, therefore a greater expense. If work equals Volts times Amps, then a higher voltage will require smaller wire to accomplish the same work.


Single-phase components typically are larger, so equipment utilizing a three-phase source have a smaller foot print and may be cheaper to purchase. Higher voltage equipment, regardless of number of phases, also has a smaller foot print, are lighter and often cheaper to purchase and install.


Switch gear for larger utilization equipment can be very expensive, however in this case, three-phase is typically cheaper to purchase and install.


Load balancing is somewhat more complex for three-phase systems, because most ?electricians? are installers and do not have a comfortable grasp of technical aspects of the first six paragraphs of this post. So there is a legitimate consideration of finding the right firm to provide support or maintenance of your three phase system.


There are two types of three phase systems, being Delta and Wye. In a Delta, the three phases are connected in series. In a Wye, the three phases are connected with one end all tied to Ground.


In heavy industry, Deltas and Wyes are equally common and are normally over 600 Volts, frequently as high as 13,800Volts. In light industry, the Wye is most common and usually 600 Volts or less. In light commercial the Delta is most common and often 480 or 240 Volts.


A very common service used in Strip malls, light manufacturing and rural settings is the Open Delta. This is when the power company uses two phases to make three. As a 4 wire Delta, it has a single-phase service contained within the three-phase installation. Normally a 240 Volt Delta, it has the same service as your house by center tapping one phase, yet can provide 240 Volt three-phase power as well. The electric utility likes this because it holds their costs down by eliminating the need for running all three phases over some great distance and uses only two transformers.


This gives the customer the benefit of a common single phase voltage at any connection to the system and still provide the 120/240 Volt single-phase for convenience outlets. 240 volt motors can be connected across any two lines, or 240 Volt, Three-Phase motors will be connected to all three lines. Office outlets and convenience outlets throughout the facility will be connected on one, of two particular lines to ground. The bad part here is the ?Hot Leg,? or ?Wild Leg? that has a higher Line to Neutral Voltage to ground. Incompetent persons calling themselves electricians can get into big trouble being unaware of this phenomenon

Phase is a term used to indicate the time or distance relationship between two waveforms, such as voltage -to-current or voltage-to-voltage. When two waveforms are in step with each other, they are said to be in phase with each other.

In a purly resistive ac curcuit, the current and voltage are in phase. This means that, at every instant, the current is exactly in step with the applied voltage. They BOTH reach their zero and peak values at the same time.

Phase are often expressed in degrees: one full waveform is equal to 360 degrees. For example, a three phase generator has each of its windings out of phase with each other by 120 degrees.

Ok with that said you have "crudly " lets say each PHASE of a single phase system has its own waveform that we as electricians TRY to balance out so the potential value is zero at the exact same time of the sinusoidal wave form.....other things can effect this like Lag and Lead and well that just goes to much into electrical theory for this site..so I will digress...

Anyway....what you are dealing with is Single Phase and Three Phase....the I THINK I explained the single phase above.....


--
Paul W. Abernathy- NACHI Certified
Electrical Service Specialists
Licensed Master Electrician
Electrical Contractor
President of NACHI Central Virginia Chapter
NEC Instructor
Moderator @ Doityourself.com
Visit our website- www.electrical-ess.com

Originally Posted By: bking
This post was automatically imported from our archived forum.



Paul, Good informative post,


So we are in agreement that 2 phase terminolgy is wrong, I prefer to refer to each SE feed as a LEG, (two legs and a neutral)

This brings up a good question....

With a normal Residential system and say 20 amps of current on one leg, the current on the neutral is 20 amps and the current on the GEC is zero.
I measured this so I know it was 0.00 Amps.

Why would not at least some of the neutral current pass on to the local ground rod?


--
www.BAKingHomeInspections.com

Originally Posted By: mtimpani
This post was automatically imported from our archived forum.



my head hurts



Thank you, MarkTimpani


www.pridepropertyinspections.com

Originally Posted By: pabernathy
This post was automatically imported from our archived forum.



The Equipment Grounding Conductors under normal conditions carry NO current. The only time they carry current is under abnormal conditions when an electrical appliance or piece of electrical equipment is faulty and has become a potential shock or fire hazard. Under a fault condition the grounding conductor that is connected to the outer shell or sheet metal of the equipment or appliance must be able to provide a very low resistance path back to the source of the power(utility company’s transformer) so that enough current will flow causing a breaker or fuse to open the circuit and automatically disconnect the hazard from the system.


It is NOT the purpose of this equipment grounding system to send current through the ground. Sending equipment fault currents through the earth can be a fatal misunderstanding of how a grounding system works. For the most part, the only time you intentially send current into the earth is during a lightning strike or line surge due to a nearby lightning strike.

For the breaker or fuse to operate the path of an equipment fault must be much more direct than sending it through the earth back to the transformer. In a romex(non-metallic sheathed cable) system there is a bare conductor. In a conduit/raceway system the metal of the conduit or raceway provides the path.

The mis-conception is that voltage is trying to get to ground when in fact it is trying to get back to the source...the resistance path to ground happens when voltage in excess of the return voltage to the transformer...in cases of lightning and line surge......again many are mis-informed about the use of a ground rod thinking it is for the electrical system when in fact it is not....

Hope this explains it......If you still need more details please ask...

FYI...in some cases you can read voltage on the grounding conductor because of a system problem, leaking voltage or a short in the casing of a possible appliance....and so on.

More FYI.. it is known that 2-phase" is sometimes incorrectly used as referring to 240 volt centertap usable to make separate 120 volt circuits. True 2-phase involves circuits 90 degrees apart, meaning approx. 169 volts between 120 volt "hots" of the different phases.


--
Paul W. Abernathy- NACHI Certified
Electrical Service Specialists
Licensed Master Electrician
Electrical Contractor
President of NACHI Central Virginia Chapter
NEC Instructor
Moderator @ Doityourself.com
Visit our website- www.electrical-ess.com

Originally Posted By: bking
This post was automatically imported from our archived forum.



I have heard of cases where almost all circuit breakers in a panel tripped due to nearby lightning. Obviously there was no actual overcurrent conditions on all of these circuits so the breakers must have a trip response to a strong magnetic field. I have read that breakers only get tested with magnetic fields in the factory and that is why they usually are in the tripped position when they are new.



www.BAKingHomeInspections.com

Originally Posted By: pabernathy
This post was automatically imported from our archived forum.



Quote:
I have read that breakers only get tested with magnetic fields in the factory and that is why they usually are in the tripped position when they are new.


Now that I could not answer for you..I do know they test them in a overload situation as I did a tour once of a Cutler Hammer Factory and it showed them testing........at the time I was their 200A mains were being tested....large POPS on them babies.

The concept of the lightning issue ahs more to do with back feeding of large amounds of amperage on the line that ends up being a line surge back into the house which usually takes out more than one house in this case......lightning strikes to a house directly is a individual issue as well not the exact same occurance as a Line Surge.


--