What do you think about this pic?

The main feed wires were to short so they pig tailed…

Not a problem. Splices are contained in a big junction box called a Service Panel.

Gosh I was just going to ask what the big green box outside was for and forgot you are out west where they make you stand outside to reset your breakers.:slight_smile:

The pigtail is OK as far as I know.Just makes you wonder.

I see merretts on several wires. Had an electrician with me on my last HI. He was concerned about merrett on a wiring in the panel. Said it was OK because the wire was terminated. No longer live.
Any information would be appreciated.

Composition is a bit odd. The subject matter kind of boring. A little bit of keystone distortion is present in the image. Contrast and exposure are pretty good though.

Mark. Was the panel changed out at some time or do you think this was the original install?

I have a referral coming down for you. They should be leaving WA in about 30 days upon their home closing. Will advise when I have firm dates.

Judging from the lack of matching paint it appears that they just changed out the panel. The splices are permitted but the work in general is very sloppy. If this is in a wet location then the nipple between the meter enclosure and the panel is a problem unless there is a sealing locknut on the panel side. Also that nipple would require bonding with something other than standard locknuts (that could be within the meter enclosure and therefore not visible). It’s also hard to tell if the neutral bus is bonded to the panel enclosure and the bare GEC’s should be terminated on the neutral bus not the ground bus. Also the large neutral near the bottom is not properly terminated.

Stephen, new panel, thanks for the referral. Robert good info thank you. Chuck thanks for your opinions.

Robert thanks for the help, Stephen, new panel, Chuck thanks for your opinions…

Since this a new panel was there a permit and inspection done?

not sure, done a couple years ago

Why would you need one if the panel is bonded?? Or do you mean if you put a rubber gasket on it.

A metallic service raceway (on the *line *side of the service disconnect) is required to be bonded to the enclosure or grounded (neutral) conductor. Standard locknuts are not permitted to perform this bonding. That would require a bonding locknut, bonding wedge or bonding bushing, etc. As I stated, in the photo it is not visible on the nipple entering the panel but very well could be on the meter side of the nipple. This bonding is only required at one end of the raceway.

What is the specific difference betweeen the bonding lock nut and the standard lock nut? Other then a screw… and how does the difference affect the bonding principles of the locknut function?

I still have never understood that one. Its like grounding a gas meter that has 70 ft of metal line buried in the dirt…

Good question. I think that the obvious answer is that the bonding locknut simply works better since it has a sharp screw cutting directly into the metal of the enclosure. But I’m not sure if the UL standard for carrying fault current is any different between the two when they’re properly installed.

I personally have seen very few of them here. Same ol story, no big deal. Guess it is not of big importance to most even though it is still not correct. I doubt I would get very many to change it if I wrote it up to begin with.

I see a lot of panels here with splices like that where Al was used as the main feed with squeeze connections to copper pig tails so that Al does not have to be under the screw lugs

Neutral Bonding Jumper. This would be a good time to talk about the neutral bonding jumper. The neutral and the ground can only be bonded in one location in a residential service, and that is in the main *panel
Hope I am talking about the threads question.
*

Are you saying this applies only in a residential services, meaning it would be permitted in other installations?

Why has nobody mentioned that the main feed wires aren’t even spliced?