As long as no windows in garage door, E. Insured will get the minor credit for rest of house glazed openings being protected. For A-D must be impact rated large or small missile, and appears your garage door is cyclic and pressure only, non impact.
No windows in the Garage door, nor skylights.
I agree and would have marked E in such a case.
However, an agent informed me that a reinspector is Changing these to a B rating… The client had aninaccurate inspection that was marked A.
Exactly the same shutter situation I described.
Upon reinspection, the rating was changed from A to B? Not E.
Since the OHD is not impact rated, you, by default, have to select E. D asks for wind-borne debris protection, which a wind-rated door does not provide.
You already know that the panels are MDC Approved, Large Missle Impact. Therefore, if you select D you are not reporting the truth.
I agree that “E” is correct, but don’t forget to tell the policyholder that since, " All windows and entry doors are protected by shutters", they are now in violation of fire safety codes, no egress. Have them buy a chain saw…:razz:
Florida Building Code: Chapter 10 Section 1008.1.3.6 Means of Egress
The temporary installation or closure of storm shutters, panels or other approved hurricane protection devices shall be permitted on emergency escape and rescue openings in group R (Residential) occupancies during the threat of a storm. Such devices shall not be required to comply with the operational constraints of section 1025.4. While such protection is provided, at least one means of escape shall be provided. This means of escape shall be within the first floor of the dwelling or dwelling unit and shall not be located within a garage without a side-hinged door leading directly to the exterior. Occupants in any part of the dwelling or dwelling unit shall be able to access the means of escape without passing through a lockable door not under their control.